MSTR Message to Read 6 Digit Registers
I am wondering if anyone has any experience polling a ClickPLC which uses 6 digit registers, using a SCADAPACK 350 using TelepaceStudio as the Master Polling Device. Typically I would use MSTR Messaging however the CLICK PLC uses 6 digit registers.
For example, the CLICK PLC uses register 428673 for analog input 1 (floating point). I can poll this PLC using GeoSCADA but the outstation has to be changed from 5 digit addressing to 6 digit addressing.
Does the ScadaPack have the ability to poll this 6 digit register?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-1702:13 AM
In the SCADAPack E Configurator when you add a Modbus Slave Device there is a Register Addressing field to specify whether 5 digit or 6 digit addressing is used.