I am wondering if anyone has any experience polling a ClickPLC which uses 6 digit registers, using a SCADAPACK 350 using TelepaceStudio as the Master Polling Device. Typically I would use MSTR Messaging however the CLICK PLC uses 6 digit registers.
For example, the CLICK PLC uses register 428673 for analog input 1 (floating point). I can poll this PLC using GeoSCADA but the outstation has to be changed from 5 digit addressing to 6 digit addressing.
Does the ScadaPack have the ability to poll this 6 digit register?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-17 02:13 AM
In the SCADAPack E Configurator when you add a Modbus Slave Device there is a Register Addressing field to specify whether 5 digit or 6 digit addressing is used.