Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
Howard1
Ensign
Ensign
0 Likes
6
1968

Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

We're looking to deploy a Virtual ViewX solution for a customer to support 25 concurrent client connections.  The GeoSCADA installation doco recommends (for 20 clients) host with CPU passmark=15000, 2D Graphics passmark 300, 10 Cores, 32GB RAM, 1GB network.  I'm interested in whether anyone has any real life experience deploying a VVX server for this order of clients and can offer any insight or pit-falls to watch out for when spec'ing the server.  What have you used for the host - physical or virtual, if virtual with dedicated graphics resources, how successful was this in practice?  I'm really just wanting to draw on others experience to avoid known issues and propose best solution for the customer, as I haven'y personally deployed the VVX solution before...  Thanks! 

 

 

Tags (1)

Accepted Solutions
AdamWoodland
Commander Commander
Commander
5
1923

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

I haven't tried as high as 25, max so far is 10 using 8 cores/16GB of RAM. So far no complaints have made it my way, yet, but I'm not the active implementer or user of the system.

 

Some risk might be able to be managed by using a load balancer (e.g. cloud load balancer, web app firewall, or even just a small nginx on Linux) in-front of multiple servers to manage load. Haven't tried this so there may be some gotchas, but on paper it should/could work. It does use websockets so that might cause some problems as it did with OWASP rules in the WAF when I tried those.

See Answer In Context

Tags (1)
sbeadle
Janeway Janeway
Janeway
4
1896

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

Yesterday I saw 50 (yes, 50!) VVX web clients log in to an Azure F16v2 Server - 16 core CPU with SSD and 32Gb RAM.

Performance was tight, and complex mimics would stress the server a lot, but we had each client up with an alarm banner and new mimic changes up every 5 seconds. An F32 server with more cores would handle it better.

 

Note: to get this up and running with this number of clients, you must have a separate VVX server from Geo SCADA, and change the settings for sessions. Go to the VVX Manager applet. pick the Sessions tab. At the bottom choose "Multiple browser per session" and set a session count of 5. (All 50 users are still kept separate, but this allocates server resources to enable this sort of scalability).

 

See Answer In Context

Tags (1)
BevanWeiss
Spock
Spock
0 Likes
2
1873

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

@sbeadle 

That is great to hear.

Was this with the default ViewX logging still enabled?

 

In some recent testing we've found the ViewX logging to be quite the bottle neck in general ViewX performance.

It would be great if you had the opportunity to disable logging on this server to just compare the performance.

 

The NVMe RAID SSDs that the F16v2 (and F32) use should obviously mitigate many of the disk 'media' read/write performance issues, but I'm running an NVMe SSD setup on my computer also, and just the disk subsystem impact (i.e. all the code executed to get a byte from the application to the disk) seemed to have a significant negative impact on performance. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Tags (1)
6 Replies 6
AdamWoodland
Commander Commander
Commander
5
1924

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

I haven't tried as high as 25, max so far is 10 using 8 cores/16GB of RAM. So far no complaints have made it my way, yet, but I'm not the active implementer or user of the system.

 

Some risk might be able to be managed by using a load balancer (e.g. cloud load balancer, web app firewall, or even just a small nginx on Linux) in-front of multiple servers to manage load. Haven't tried this so there may be some gotchas, but on paper it should/could work. It does use websockets so that might cause some problems as it did with OWASP rules in the WAF when I tried those.

Tags (1)
sbeadle
Janeway Janeway
Janeway
4
1897

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

Yesterday I saw 50 (yes, 50!) VVX web clients log in to an Azure F16v2 Server - 16 core CPU with SSD and 32Gb RAM.

Performance was tight, and complex mimics would stress the server a lot, but we had each client up with an alarm banner and new mimic changes up every 5 seconds. An F32 server with more cores would handle it better.

 

Note: to get this up and running with this number of clients, you must have a separate VVX server from Geo SCADA, and change the settings for sessions. Go to the VVX Manager applet. pick the Sessions tab. At the bottom choose "Multiple browser per session" and set a session count of 5. (All 50 users are still kept separate, but this allocates server resources to enable this sort of scalability).

 

Tags (1)
Howard1
Ensign
Ensign
0 Likes
0
1883

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

Thanks Steve - that is reassuring to hear!

Tags (1)
BevanWeiss
Spock
Spock
0 Likes
2
1874

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

@sbeadle 

That is great to hear.

Was this with the default ViewX logging still enabled?

 

In some recent testing we've found the ViewX logging to be quite the bottle neck in general ViewX performance.

It would be great if you had the opportunity to disable logging on this server to just compare the performance.

 

The NVMe RAID SSDs that the F16v2 (and F32) use should obviously mitigate many of the disk 'media' read/write performance issues, but I'm running an NVMe SSD setup on my computer also, and just the disk subsystem impact (i.e. all the code executed to get a byte from the application to the disk) seemed to have a significant negative impact on performance. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
sbeadle
Janeway Janeway
Janeway
0 Likes
1
1693

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

ViewX logging was not enabled. However, there are changes proposed to logging to make it more granular and less noisy.

BevanWeiss
Spock
Spock
0 Likes
0
1653

Re: Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

I see that GSE 2020 already includes some of the 'less noisy' works.  The cached registry read logging, which had been one of the huge performance impacts from my bench testing, is now suppressed.

 

Definitely looking forward to seeing more of the configurable logging with ViewX.

For the most part we don't have issues, so would prefer to be able to configure it to have very low overhead (i.e. disabled / minimal logging).

And we typically only report issues when they are reproducible, or at least recurring.  And in those situations we can enable logging for a period (and suffer the performance hit) to obtain detailed 'error' results.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..