[Imported] View RAW value from Modbus Analog Input
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-0501:12 PM. Last Modified: 2023-05-0312:35 AM
[Imported] View RAW value from Modbus Analog Input
>>Message imported from previous forum - Category:ClearSCADA Software<< User: florian, originally posted: 2018-10-25 16:04:54 Id:233 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
-------------------------------
**_MikeForshock:_** **_Have been digging through the ClearSCADA database tables attempting to find abetter solution than creating two analog points or a single analog point and a function block (logic) program for scaling._**
**_Would prefer to use the internal scaling for simplicity and point savings, but need to have the RAW value from the device visible for scaling reference. Cannot find the value in any table I have researched._**
**_Any suggestions?_**
**_Thanks in advance,_**
**_Mike_**
-----------------------
sbeadle: Hi Mike,
I don't believe the raw value is written anywhere, and it certainly will not be stored historically.
You could use a Calculation Analogue Point to store this value - using a formula which incorporates the point's scaling properties to 'reverse' the scaling calculation and store unscaled. This would allow you to store the unscaled value in history for future reference.
Steve
-------------------------------------------
dmercer: If you only need to display the raw value, and you don't need history or alarming on it, then you could just use a mimic expression to do the reverse calculation on the display.