[Imported] Search Keys -- Good or Bad?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Search Keys -- Good or Bad?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
323
AndrewScott
Admiral AndrewScott
118
BevanWeiss
Spock BevanWeiss
100
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxureβ„’ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-26 02:04 PM . Last Modified: β€Ž2023-05-03 12:21 AM

0 Likes
1
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-26 02:04 PM . Last Modified: β€Ž2023-05-03 12:21 AM

[Imported] Search Keys -- Good or Bad?

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: tfranklin, originally posted: 2019-09-30 16:26:51 Id:528
I'm looking to start some discussion on the topic of Search Keys. They seem really beneficial when used properly. That said, we've never really used them in the past so my exposure to them is fairly limited. From what I can tell, a search key is a new metadata field that acts (when Tag is checked) a value map. Search keys are required to be unique if Tag is checked, so I'm going to assume they're indexed. With tag checked, you get some new liberties with expressions where instead of full path you can use searchkeyhere.propertyhere. Pretty neat stuff.

For those who have insights into Search Keys, I ask the following:

1. What're the negative impacts of search keys? Ex: Are they treated like indirect animations where they should really be avoided unless used wisely? Do they cause excess CPU strain?
2. Do search keys impact client load times?
3. What are some clever ways you've seen search keys used?
4. What are some really bad ways you've seen search keys used?
5. Why would anybody use search keys with tag unchecked?
6. Is there an advantage to having a search key with tag unchecked vs a normal string metadata field for Config/Data?

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-26 02:05 PM

0 Likes
0
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-26 02:05 PM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2019-09-30 22:28:00
Search keys are the original metadata, the standard metadata fields only came into the product about 12 years ago based on the limitations of search keys.

They're great when used correctly, basically without the tag they're an indexed lookup, with the tag ticked they're a unique indexed lookup. What that means is SQL queries that use them in there WHERE clause are more efficient that those with a standard string metadata field (which isn't indexed).

To answer your questions:

1. Search keys are only stored in the config stream, and as they have an index they use more CPU effort when updating. What this means really is if the content of the fields are changing 'often' then search keys are probably not the best option (compared to say standard string metadata fields against the Data stream). One of the whole keeping Config and Data streams separate was to minimize the data flushed to disk with each point value update, and back with ClearSCADA on NT4 days the disk impacts was significant. Now days disks access is so much faster the actually impact of Data and Config streams on disk is minimal but still needs to be considered for other things like network bandwidth.

2. Depends what you mean by client load times. The indexed efficiencies of search keys should mean SQL queries are quicker for clients to retrieve from the server so the perceived performance should improve

3. Common uses are for say the old tag names from imported systems, i.e. ClearSCADA now has its full OPC name (Group.Group.Group.Object) whereas the tag option allows an alternative mapping of names, i.e. P123SN23 (which may be what old systems may still use to access data via OPC-DA). Not sure of any specifically clever ways, it is all about planning how your SQL queries will query and planning your metadata accordingly

4. Anything that is frequently updated. As mentioned above any really old ClearSCADA systems will likely all be search keys, and so those are bound to have some sub-optimal setup (by current standards) solutions there. Can't think of anything specifically though.

5. When tag is checked you're forcing the content for that search key to be unique per object, that has useful cases but also means you couldn't have some grouping. For example you may store in the search key some common attribute across many parts of the database, an example could be the 'owner' of the asset, and different owners due to maybe contractual or commercial reasons could be dotted across the database. Using a search key could allow a much more efficient search to be done. On a database of a few thousand objects then a table scan rather than a indexed lookup is probably a second or so difference, but when you're dealing with databases of 200,000 to a million objects the impact is significant. Last time I checked I believe you can only have one search key set as tag, so other search keys have to have that option untagged.

6. See above, search keys are indexed, so SQLs using those fields are much quicker. When you start using large databases this becomes very important. But using them at the wrong time on a large database may also cause you more problems


Reply From User: tfranklin, posted: 2019-09-30 23:08:48
[at]adamwoodland very interesting stuff! I can definitely see some benefits to moving a few fields we utilize over to search keys. I'll put some thought into this and see what I can break.

One quick question -- I was browsing the help file and noticed an article for Historic Search Keys. In the 10 minutes I spent clicking around, I couldn't find a way to actually implement one and get it to show up as mentioned in help. Any ideas on what those are vs a normal search key, or how to implement one?


Reply From User: adamwoodland, posted: 2019-09-30 23:47:53
Unfortunately its not a case of a simple change, you'll have to create a new field, copy things over between fields (including setting property overrides as necessary) and then deleting the old field and renaming... frankly a pain and something you probably only really want to do if you are having performance issues with SQL. A dodgy hack of the metadata XML file with a cold restart never used to work and I assume still won't πŸ™‚

I wasn't aware of the term historic search keys so I looked it up. Looks to be the same as search keys, just if you also enable historic (so limited to points) you can see them under search keys in the "OPC Historic" toolbar (much the same as you can see them in the "OPC Data" toolbar under search keys)


Reply From User: tfranklin, posted: 2019-10-01 00:51:57
Completely agree. I'm just considering it all for new builds and making them more efficient. I've converted fields in the past from one data type to another and succeeded in blowing up the server. Lessons were learned. It has been some years but it was indeed a dodgy hack and converting a string to a reference field. I'd rate the experience as a 0/10, do not recommend.


Reply From User: andrewscott, posted: 2019-10-01 08:45:10
The January 2019 monthly updates (for 6.78, 6.79 and 6.80) contain fixes for several problems with converting metadata fields between different types, including converting string fields (containing object names) to reference fields.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-26 02:05 PM

0 Likes
0
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-26 02:05 PM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2019-09-30 22:28:00
Search keys are the original metadata, the standard metadata fields only came into the product about 12 years ago based on the limitations of search keys.

They're great when used correctly, basically without the tag they're an indexed lookup, with the tag ticked they're a unique indexed lookup. What that means is SQL queries that use them in there WHERE clause are more efficient that those with a standard string metadata field (which isn't indexed).

To answer your questions:

1. Search keys are only stored in the config stream, and as they have an index they use more CPU effort when updating. What this means really is if the content of the fields are changing 'often' then search keys are probably not the best option (compared to say standard string metadata fields against the Data stream). One of the whole keeping Config and Data streams separate was to minimize the data flushed to disk with each point value update, and back with ClearSCADA on NT4 days the disk impacts was significant. Now days disks access is so much faster the actually impact of Data and Config streams on disk is minimal but still needs to be considered for other things like network bandwidth.

2. Depends what you mean by client load times. The indexed efficiencies of search keys should mean SQL queries are quicker for clients to retrieve from the server so the perceived performance should improve

3. Common uses are for say the old tag names from imported systems, i.e. ClearSCADA now has its full OPC name (Group.Group.Group.Object) whereas the tag option allows an alternative mapping of names, i.e. P123SN23 (which may be what old systems may still use to access data via OPC-DA). Not sure of any specifically clever ways, it is all about planning how your SQL queries will query and planning your metadata accordingly

4. Anything that is frequently updated. As mentioned above any really old ClearSCADA systems will likely all be search keys, and so those are bound to have some sub-optimal setup (by current standards) solutions there. Can't think of anything specifically though.

5. When tag is checked you're forcing the content for that search key to be unique per object, that has useful cases but also means you couldn't have some grouping. For example you may store in the search key some common attribute across many parts of the database, an example could be the 'owner' of the asset, and different owners due to maybe contractual or commercial reasons could be dotted across the database. Using a search key could allow a much more efficient search to be done. On a database of a few thousand objects then a table scan rather than a indexed lookup is probably a second or so difference, but when you're dealing with databases of 200,000 to a million objects the impact is significant. Last time I checked I believe you can only have one search key set as tag, so other search keys have to have that option untagged.

6. See above, search keys are indexed, so SQLs using those fields are much quicker. When you start using large databases this becomes very important. But using them at the wrong time on a large database may also cause you more problems


Reply From User: tfranklin, posted: 2019-09-30 23:08:48
[at]adamwoodland very interesting stuff! I can definitely see some benefits to moving a few fields we utilize over to search keys. I'll put some thought into this and see what I can break.

One quick question -- I was browsing the help file and noticed an article for Historic Search Keys. In the 10 minutes I spent clicking around, I couldn't find a way to actually implement one and get it to show up as mentioned in help. Any ideas on what those are vs a normal search key, or how to implement one?


Reply From User: adamwoodland, posted: 2019-09-30 23:47:53
Unfortunately its not a case of a simple change, you'll have to create a new field, copy things over between fields (including setting property overrides as necessary) and then deleting the old field and renaming... frankly a pain and something you probably only really want to do if you are having performance issues with SQL. A dodgy hack of the metadata XML file with a cold restart never used to work and I assume still won't πŸ™‚

I wasn't aware of the term historic search keys so I looked it up. Looks to be the same as search keys, just if you also enable historic (so limited to points) you can see them under search keys in the "OPC Historic" toolbar (much the same as you can see them in the "OPC Data" toolbar under search keys)


Reply From User: tfranklin, posted: 2019-10-01 00:51:57
Completely agree. I'm just considering it all for new builds and making them more efficient. I've converted fields in the past from one data type to another and succeeded in blowing up the server. Lessons were learned. It has been some years but it was indeed a dodgy hack and converting a string to a reference field. I'd rate the experience as a 0/10, do not recommend.


Reply From User: andrewscott, posted: 2019-10-01 08:45:10
The January 2019 monthly updates (for 6.78, 6.79 and 6.80) contain fixes for several problems with converting metadata fields between different types, including converting string fields (containing object names) to reference fields.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore