Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

[Imported] SMS alarm texting in virtual environment

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] SMS alarm texting in virtual environment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
115
BevanWeiss
Spock BevanWeiss
98
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 03:01 PM . Last Modified: ‎2023-05-03 12:25 AM

0 Likes
1
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 03:01 PM . Last Modified: ‎2023-05-03 12:25 AM

[Imported] SMS alarm texting in virtual environment

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: Industrial951, originally posted: 2019-04-18 18:26:48 Id:412
Hello,
I am looking for some guidance on what hardware to use regarding SMS alarm texting. We have a hot pair standby in a virtual environment. What are my options for an SMS modem that will work with ClearSCADA? I'm assuming it will have to be some type of network based SMS modem and not a serial based one.

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 03:02 PM . Last Modified: ‎2023-04-25 10:33 PM

0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 03:02 PM . Last Modified: ‎2023-04-25 10:33 PM

>>Responses imported from previous forum


Reply From User: dmercer, posted: 2019-04-22 23:31:36
I've used the Maestro M100 and the Intercel Ultra eSAM in the past for SMS from ClearSCADA. The Maestro is serial and the Intercel uses ethernet.


Reply From User: JesseChamberlain, posted: 2019-04-23 02:32:45
We have a resource center page with some relevant info [here](https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Stay-Informed/ba-p/279086 "here").


Reply From User: adamwoodland, posted: 2019-04-28 22:29:50
Also some telcos provide an email address you can send to that translates email to SMS, some telcos provide this for free, some don't.

That email to SMS solution typically provides much more flexibility in virtual environments as you don't need to worry about a physical device, and also is typically better from a security point of view as you have one less interface into your system and what is being sent can be audited properly.


Reply From User: GregYYC, posted: 2019-05-09 13:49:24
[at]adamwoodland said:
Also some telcos provide an email address you can send to that translates email to SMS, some telcos provide this for free, some don't.

That email to SMS solution typically provides much more flexibility in virtual environments as you don't need to worry about a physical device, and also is typically better from a security point of view as you have one less interface into your system and what is being sent can be audited properly.

I second this opinion! Attaching physical equipment to a virtual world is clunky, requires additional software and can be challenging in a HA cluster environment. It's possible, but usually requires some finesse.

If you can leverage SMS via email, the solution will be easier to manage and troubleshoot.


Reply From User: geoffpatton, posted: 2019-05-09 14:07:02
keep in mind that email to SMS does not support acknowledging alarms.


Reply From User: BevanWeiss, posted: 2019-05-13 00:46:48
There are a number of AT over Ethernet compatible SMS Paging Modems now available.
The Intercel eSAM and eSAM Ultra are such.
We've also tested the Robustel R3000 with success (which also has the benefit of being a dual SIM modem).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 03:02 PM . Last Modified: ‎2023-04-25 10:33 PM

0 Likes
0
1325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 03:02 PM . Last Modified: ‎2023-04-25 10:33 PM

>>Responses imported from previous forum


Reply From User: dmercer, posted: 2019-04-22 23:31:36
I've used the Maestro M100 and the Intercel Ultra eSAM in the past for SMS from ClearSCADA. The Maestro is serial and the Intercel uses ethernet.


Reply From User: JesseChamberlain, posted: 2019-04-23 02:32:45
We have a resource center page with some relevant info [here](https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Stay-Informed/ba-p/279086 "here").


Reply From User: adamwoodland, posted: 2019-04-28 22:29:50
Also some telcos provide an email address you can send to that translates email to SMS, some telcos provide this for free, some don't.

That email to SMS solution typically provides much more flexibility in virtual environments as you don't need to worry about a physical device, and also is typically better from a security point of view as you have one less interface into your system and what is being sent can be audited properly.


Reply From User: GregYYC, posted: 2019-05-09 13:49:24
[at]adamwoodland said:
Also some telcos provide an email address you can send to that translates email to SMS, some telcos provide this for free, some don't.

That email to SMS solution typically provides much more flexibility in virtual environments as you don't need to worry about a physical device, and also is typically better from a security point of view as you have one less interface into your system and what is being sent can be audited properly.

I second this opinion! Attaching physical equipment to a virtual world is clunky, requires additional software and can be challenging in a HA cluster environment. It's possible, but usually requires some finesse.

If you can leverage SMS via email, the solution will be easier to manage and troubleshoot.


Reply From User: geoffpatton, posted: 2019-05-09 14:07:02
keep in mind that email to SMS does not support acknowledging alarms.


Reply From User: BevanWeiss, posted: 2019-05-13 00:46:48
There are a number of AT over Ethernet compatible SMS Paging Modems now available.
The Intercel eSAM and eSAM Ultra are such.
We've also tested the Robustel R3000 with success (which also has the benefit of being a dual SIM modem).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore