[Imported] Pick Action Script.

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Pick Action Script.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 03:05 PM . Last Modified: ‎2023-05-03 12:25 AM

0 Likes
1
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 03:05 PM . Last Modified: ‎2023-05-03 12:25 AM

[Imported] Pick Action Script.

>>Message imported from previous forum - Category:Scripts and Tips<<
User: ROVSCADAENGINEER, originally posted: 2019-04-23 01:12:08 Id:415
I am wanting to assign an SQL script to a pick action on a drop down menu which when selected runs an SQL script to check how many times the reset has been actuated in a certain timeframe.

Then I want to use a pick action configuration which allows the pick action to control/actuate the button based on how recent the item was actuated.

The purpose behind this is to ensure that pumps are not being reset so frequently and causing overloads on the armatures.

Does anyone have any examples of scripting they can upload to this question so that I can get an understanding of how this might work or be implemented?

Many thanks.

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 03:06 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 03:06 PM

>>Responses imported from previous forum


Reply From User: ROVSCADAENGINEER, posted: 2019-04-24 00:35:24
![]((see attachments below) 1a/58r1sl7u8ccf.png "")

I have tried executing this however am not really fully understanding the help provided in the clearSCADA examples.

****my code for the script is. ****

Set Objectpoint = Server.FindObject(Paget.Test mimics.script testing.Pump Symbol + "Reset")
objectpoint.Interface.Override 1

 

Attached file: (editor/1a/58r1sl7u8ccf.png), script2.PNG File size: 74840


Reply From User: ROVSCADAENGINEER, posted: 2019-04-24 02:37:03
I have got it partially working on a test point. I just need to bring in a Count from an SQL query into the IF logic now. I am wanting to use an if statement based on a query to display the number of actuations of the point in a given timeframe.

Dim iResponse
iResponse = MsgBox (sMessage, vbExclamation + vbOKCancel + vbDefaultButton1, "Warning")
If iResponse = vbOK Then
iResponse = MsgBox("Are you sure you want to reset the pump? Be sure not to overheat from excessive resets! ", vbExclamation + vbYesNo + vbDefaultButton2, "Reset the Pump?")
If iResponse = vbYes Then
Server.SetOPCValue ".Reset.CurrentValue", 1
Else
Server.SetOPCValue ".Reset.CurrentValue", 0
End If
Else
MsgBox "Action Canceled"
End If.

 

Reply From User: BevanWeiss, posted: 2019-05-07 22:03:28
I would not recommend implementing such logic within ClearSCADA. The appropriate place for this would be within the PLC / RTU which is performing the reset action itself.

Otherwise resets performed by any HMI (i.e. not ClearSCADA), or by another instance of the ClearSCADA database, or in any other way will not be properly handled.

If you are to do this, then I would recommend doing it with actual ClearSCADA Logic. You could have a bit which the user actually drives (reset request) which only actuates the actual reset output when the reset output hasn't been triggered within some time period (or other such logic).


Reply From User: ROVSCADAENGINEER, posted: 2019-05-15 23:22:54
you raise a good point Bevan. perhaps the logic can tie into a point referencing the output by this code as a workaround to simplify the proposed logic. HMI interfaces in the field directly tied to the point are not picked up by this. so tying the actual point in the RTU to this logic like you suggested would be the best workaround yeah?


Reply From User: ROVSCADAENGINEER, posted: 2019-05-16 05:31:10
that being said [at]BevanWeiss . Say I want to cover all sites or mimics that are referencing a point. Can you assign script to a digital point itself so it runs through the logic always when it is actuated? instead of placing the script on something else that is actuating the digital point itself. to cover all access buttons to the point? by applying the code on the point itself? I hope that makes sense.

 


Reply From User: ROVSCADAENGINEER, posted: 2019-05-16 05:32:12
I do understand that scada interface will not be field based though. I am talking more for the overall scada interface here.

 

Reply From User: hardin4019, posted: 2019-05-20 21:18:48
[at]ROVSCADAENGINEER said:
that being said [at]BevanWeiss . Say I want to cover all sites or mimics that are referencing a point. Can you assign script to a digital point itself so it runs through the logic always when it is actuated? instead of placing the script on something else that is actuating the digital point itself. to cover all access buttons to the point? by applying the code on the point itself? I hope that makes sense.

Assign the point as the "Trigger" of a logic's properties?


Reply From User: ROVSCADAENGINEER, posted: 2019-05-21 03:30:40
thankyou [at]hardin4019

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 03:06 PM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 03:06 PM

>>Responses imported from previous forum


Reply From User: ROVSCADAENGINEER, posted: 2019-04-24 00:35:24
![]((see attachments below) 1a/58r1sl7u8ccf.png "")

I have tried executing this however am not really fully understanding the help provided in the clearSCADA examples.

****my code for the script is. ****

Set Objectpoint = Server.FindObject(Paget.Test mimics.script testing.Pump Symbol + "Reset")
objectpoint.Interface.Override 1

 

Attached file: (editor/1a/58r1sl7u8ccf.png), script2.PNG File size: 74840


Reply From User: ROVSCADAENGINEER, posted: 2019-04-24 02:37:03
I have got it partially working on a test point. I just need to bring in a Count from an SQL query into the IF logic now. I am wanting to use an if statement based on a query to display the number of actuations of the point in a given timeframe.

Dim iResponse
iResponse = MsgBox (sMessage, vbExclamation + vbOKCancel + vbDefaultButton1, "Warning")
If iResponse = vbOK Then
iResponse = MsgBox("Are you sure you want to reset the pump? Be sure not to overheat from excessive resets! ", vbExclamation + vbYesNo + vbDefaultButton2, "Reset the Pump?")
If iResponse = vbYes Then
Server.SetOPCValue ".Reset.CurrentValue", 1
Else
Server.SetOPCValue ".Reset.CurrentValue", 0
End If
Else
MsgBox "Action Canceled"
End If.

 

Reply From User: BevanWeiss, posted: 2019-05-07 22:03:28
I would not recommend implementing such logic within ClearSCADA. The appropriate place for this would be within the PLC / RTU which is performing the reset action itself.

Otherwise resets performed by any HMI (i.e. not ClearSCADA), or by another instance of the ClearSCADA database, or in any other way will not be properly handled.

If you are to do this, then I would recommend doing it with actual ClearSCADA Logic. You could have a bit which the user actually drives (reset request) which only actuates the actual reset output when the reset output hasn't been triggered within some time period (or other such logic).


Reply From User: ROVSCADAENGINEER, posted: 2019-05-15 23:22:54
you raise a good point Bevan. perhaps the logic can tie into a point referencing the output by this code as a workaround to simplify the proposed logic. HMI interfaces in the field directly tied to the point are not picked up by this. so tying the actual point in the RTU to this logic like you suggested would be the best workaround yeah?


Reply From User: ROVSCADAENGINEER, posted: 2019-05-16 05:31:10
that being said [at]BevanWeiss . Say I want to cover all sites or mimics that are referencing a point. Can you assign script to a digital point itself so it runs through the logic always when it is actuated? instead of placing the script on something else that is actuating the digital point itself. to cover all access buttons to the point? by applying the code on the point itself? I hope that makes sense.

 


Reply From User: ROVSCADAENGINEER, posted: 2019-05-16 05:32:12
I do understand that scada interface will not be field based though. I am talking more for the overall scada interface here.

 

Reply From User: hardin4019, posted: 2019-05-20 21:18:48
[at]ROVSCADAENGINEER said:
that being said [at]BevanWeiss . Say I want to cover all sites or mimics that are referencing a point. Can you assign script to a digital point itself so it runs through the logic always when it is actuated? instead of placing the script on something else that is actuating the digital point itself. to cover all access buttons to the point? by applying the code on the point itself? I hope that makes sense.

Assign the point as the "Trigger" of a logic's properties?


Reply From User: ROVSCADAENGINEER, posted: 2019-05-21 03:30:40
thankyou [at]hardin4019

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore