[Imported] Overulling mimic drop down menu

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Overulling mimic drop down menu
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 02:53 AM . Last Modified: ‎2023-05-03 12:30 AM

0 Likes
1
1172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:53 AM . Last Modified: ‎2023-05-03 12:30 AM

[Imported] Overulling mimic drop down menu

>>Message imported from previous forum - Category:General Items<<
User: ROVSCADAENGINEER, originally posted: 2018-11-25 22:55:45 Id:326
I am working with creating some drop down menus for pumps on a mimic page. I have traced back to the dource of the original drop down menu by locating the file in template etc. When I edit the drop down menu entries to allow for pump master inhibit etc. this does not update on the mimics main page. I have checked that the digital and analogue points referenced are correct, functioning aswell and that they are in the correct folder location. still however the points do not show up?

What I am asking is if there is a way to locate the actual source of the drop down menu is without using the locate in database explorer from the mimics page. I have attached an image also. Is there any other reason I am not aware of that would cause this not to happen? I tried updating the mimics from the template and it still did not deploy objectively to each site.

Any help appreciated!

Kind regards. ![]((see attachments below) 86/nqspcmodxhcp.png "")


Attached file: (editor/86/nqspcmodxhcp.png), drop down menu.PNG File size: 18540

Attachments
Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 02:53 AM

0 Likes
0
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:53 AM

>>Responses imported from previous forum


Reply From User: ROVSCADAENGINEER, posted: 2018-11-25 23:17:25
Have also checked property overrides


Reply From User: ROVSCADAENGINEER, posted: 2018-11-26 04:50:09
this may seem like a silly question but, I am pretty stuck on this. maybe I was not very clear in my explanation. Originally I thought the issue was that the IO folder was not stored in the template and that was why the option was not appearing on the drop down menu. So inste
ad I edited the mimic in the site folder itself to directly call the IO functions from the IO folder stored in the site folder. it would make sense for this to work yet still no menu option is appearing. I am a little confused as to why this might be occurring. I have attached images with the folder structure and the settings.
.....

 

 

 

![]((see attachments below) 6n/s10cl6od0ir9.png "")
![]((see attachments below) sa/efzuvklif4fo.png "")
![]((see attachments below) b4/byaldejb59hw.png "")
![]((see attachments below) 77/94xvvszjvx2g.png "")


Attached file: (editor/6n/s10cl6od0ir9.png), 2.PNG File size: 14357

Attached file: (editor/sa/efzuvklif4fo.png), 1.PNG File size: 19942

Attached file: (editor/b4/byaldejb59hw.png), 4.PNG File size: 21009

Attached file: (editor/77/94xvvszjvx2g.png), 3.PNG File size: 112345


Reply From User: geoffpatton, posted: 2018-11-26 14:55:37
Could your user's control permissions be messed up?


Reply From User: ROVSCADAENGINEER, posted: 2018-11-26 21:12:52
Good question.. No unfortunately as we have tried with two different users.


Reply From User: BevanWeiss, posted: 2019-01-03 21:20:55
How many levels of templating is your instance under?
The SymbolBasic mimic is within an instance of something, do you have DocumentContent overridden in the template?
Where are you editing the symbol, in the template or the instance?


Reply From User: hardin4019, posted: 2019-04-08 16:41:26
If you open an instance of the pump Mimic you are working with, can you edit the mimic? There is a Property Override that will allow you to edit mimics inside of an instance of a template. If this is turned on, then the Instance(s) of the Mimic will not update with any changes saved to the Template, even if you do a Repair Instance. The only way to fix this that I am aware of is to manually edit the Mimic, or to copy and paste in the changes from the Template.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 02:53 AM

0 Likes
0
1172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:53 AM

>>Responses imported from previous forum


Reply From User: ROVSCADAENGINEER, posted: 2018-11-25 23:17:25
Have also checked property overrides


Reply From User: ROVSCADAENGINEER, posted: 2018-11-26 04:50:09
this may seem like a silly question but, I am pretty stuck on this. maybe I was not very clear in my explanation. Originally I thought the issue was that the IO folder was not stored in the template and that was why the option was not appearing on the drop down menu. So inste
ad I edited the mimic in the site folder itself to directly call the IO functions from the IO folder stored in the site folder. it would make sense for this to work yet still no menu option is appearing. I am a little confused as to why this might be occurring. I have attached images with the folder structure and the settings.
.....

 

 

 

![]((see attachments below) 6n/s10cl6od0ir9.png "")
![]((see attachments below) sa/efzuvklif4fo.png "")
![]((see attachments below) b4/byaldejb59hw.png "")
![]((see attachments below) 77/94xvvszjvx2g.png "")


Attached file: (editor/6n/s10cl6od0ir9.png), 2.PNG File size: 14357

Attached file: (editor/sa/efzuvklif4fo.png), 1.PNG File size: 19942

Attached file: (editor/b4/byaldejb59hw.png), 4.PNG File size: 21009

Attached file: (editor/77/94xvvszjvx2g.png), 3.PNG File size: 112345


Reply From User: geoffpatton, posted: 2018-11-26 14:55:37
Could your user's control permissions be messed up?


Reply From User: ROVSCADAENGINEER, posted: 2018-11-26 21:12:52
Good question.. No unfortunately as we have tried with two different users.


Reply From User: BevanWeiss, posted: 2019-01-03 21:20:55
How many levels of templating is your instance under?
The SymbolBasic mimic is within an instance of something, do you have DocumentContent overridden in the template?
Where are you editing the symbol, in the template or the instance?


Reply From User: hardin4019, posted: 2019-04-08 16:41:26
If you open an instance of the pump Mimic you are working with, can you edit the mimic? There is a Property Override that will allow you to edit mimics inside of an instance of a template. If this is turned on, then the Instance(s) of the Mimic will not update with any changes saved to the Template, even if you do a Repair Instance. The only way to fix this that I am aware of is to manually edit the Mimic, or to copy and paste in the changes from the Template.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore