[Imported] Filtered version of Alarm State and Severity on CGroup

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Filtered version of Alarm State and Severity on CGroup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:16 PM . Last Modified: ‎2023-05-03 12:28 AM

0 Likes
1
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:16 PM . Last Modified: ‎2023-05-03 12:28 AM

[Imported] Filtered version of Alarm State and Severity on CGroup

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: AaronJust, originally posted: 2019-02-06 04:55:29 Id:361
In the ClearSCADA database, objects of type CGroup have data fields AlarmSeverity and AlarmState - which aggregate the alarm severity and states of ****all**** children of the group.

I would like to do something similar, only the result is based on only ****some**** children of the group (i.e. only the alarm severity and state of children matching a certain criteria).

I can generate logic that achieves what I want (i.e. query all database objects matching my criteria, and analyse AlarmSeverity and AlarmState as I require, saving the result to an internal point), but I don't think that's ideal to use as an animation for 200+ different groups.

Is there a way (e.g. custom dynamic metadata, etc.) where this can be calculated on a CGroup which could then be accessible as an OPC Tag in an expression?

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:16 PM

0 Likes
0
1388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:16 PM

>>Responses imported from previous forum


Reply From User: dmercer, posted: 2019-02-06 21:59:06
It is feasible to create a custom metadata property for CGroup and then use a structured text program to set that value for each group where it is required. These are accessable like any other OPC tag. You 'll have to do some testing on how it effects the performance of the server.


Reply From User: BevanWeiss, posted: 2019-02-07 00:41:03
Doing SQL from within Logic is frowned upon, and can cause DB performance issues.
The 'ideal' performance-wise method would be to have a set of Calculation Points with each sub-point of interest's AlarmSeverity/AlarmState referenced in the expression so that the calculation only triggers on change.
But this would be horrible from a configuration perspective.
It would almost border on custom driver territory, which would register for notifications on certain points / groups and then update some custom metadata as required. But it would be painful to do what you want all the same...


Reply From User: adamwoodland, posted: 2019-02-07 02:24:53
Few other suggestions. Could use the alarm summary table somehow, but it is file based so be careful with that (i.e. with logic as per Bevan's comment)

Could do it with alarm redirection on the root group, i.e. event driven, and trigger some logic that perhaps write the alarm to some datatable as a scratch pad type thing, and then process that somehow.


Reply From User: hardin4019, posted: 2019-02-27 16:19:06
Not sure if this is resolved, or if my solution is helpful, but I have made a custom alarm screen for a client at their request. The alarm screen is split into 3 different groups of alarms, those with a "Critical Severity", second those with "Medium" or "High" severity, and the third has "Alert" and "Low" severity. Each list is the "Alarm List" type.

Just using the Alarm List doesn't give you a count of Uncleared / Unacknowledged, or Uncleared / Acknowledged alarms the way the built in Alarm banner does. So I made two ODBC Queries to give me a count for each Severity grouping and display those numbers along side the Alarm List to roughly replicate the Alarm Banner.

The query looks like this;

Select
Count(ID) AS "Uncleared Unack Count"
From
CAlarm
Where
( State between 3 and 4 ) and ( Severity between 4 and 11)

Then I setup an ODBC point looking at this query, row 1, column 1. The result is the number of Uncleared and Unacknowledged alarms with a severity of 5 (alert) and 10 (Low).

Same query and ODBC point setup used for Uncleared, but acknowledged with minor changes in State and column name.

Select
Count(ID) AS "Uncleared"
From
CAlarm
Where
( State between 2 and 3 ) and ( Severity between 4 and 11)

The Query WHERE section could be used to narrow the results to only specific sub folders or alarm conditions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:16 PM

0 Likes
0
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:16 PM

>>Responses imported from previous forum


Reply From User: dmercer, posted: 2019-02-06 21:59:06
It is feasible to create a custom metadata property for CGroup and then use a structured text program to set that value for each group where it is required. These are accessable like any other OPC tag. You 'll have to do some testing on how it effects the performance of the server.


Reply From User: BevanWeiss, posted: 2019-02-07 00:41:03
Doing SQL from within Logic is frowned upon, and can cause DB performance issues.
The 'ideal' performance-wise method would be to have a set of Calculation Points with each sub-point of interest's AlarmSeverity/AlarmState referenced in the expression so that the calculation only triggers on change.
But this would be horrible from a configuration perspective.
It would almost border on custom driver territory, which would register for notifications on certain points / groups and then update some custom metadata as required. But it would be painful to do what you want all the same...


Reply From User: adamwoodland, posted: 2019-02-07 02:24:53
Few other suggestions. Could use the alarm summary table somehow, but it is file based so be careful with that (i.e. with logic as per Bevan's comment)

Could do it with alarm redirection on the root group, i.e. event driven, and trigger some logic that perhaps write the alarm to some datatable as a scratch pad type thing, and then process that somehow.


Reply From User: hardin4019, posted: 2019-02-27 16:19:06
Not sure if this is resolved, or if my solution is helpful, but I have made a custom alarm screen for a client at their request. The alarm screen is split into 3 different groups of alarms, those with a "Critical Severity", second those with "Medium" or "High" severity, and the third has "Alert" and "Low" severity. Each list is the "Alarm List" type.

Just using the Alarm List doesn't give you a count of Uncleared / Unacknowledged, or Uncleared / Acknowledged alarms the way the built in Alarm banner does. So I made two ODBC Queries to give me a count for each Severity grouping and display those numbers along side the Alarm List to roughly replicate the Alarm Banner.

The query looks like this;

Select
Count(ID) AS "Uncleared Unack Count"
From
CAlarm
Where
( State between 3 and 4 ) and ( Severity between 4 and 11)

Then I setup an ODBC point looking at this query, row 1, column 1. The result is the number of Uncleared and Unacknowledged alarms with a severity of 5 (alert) and 10 (Low).

Same query and ODBC point setup used for Uncleared, but acknowledged with minor changes in State and column name.

Select
Count(ID) AS "Uncleared"
From
CAlarm
Where
( State between 2 and 3 ) and ( Severity between 4 and 11)

The Query WHERE section could be used to narrow the results to only specific sub folders or alarm conditions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore