Import SDE
Hi,
Im trying to import .sde to check the scada graphics on to my system. I exported from the live system however when i import on to mine i can only view the mimics all the tags associated are missing.
- Labels:
-
SCADA
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-04 02:13 AM
It sounds like the SDE file doesn't include the points referenced by the animations in the mimics. When you export the configuration you need to export the group that contains both the points and mimics. Alternatively, do two (or more) exports and import the one containing the mimics last (this requires both databases have the exact same group hierarchy so all the references can be resolved during the import).
Andrew Scott, R&D Principal Technologist, AVEVA