How to set quality to bad when Modbus is down?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • How to set quality to bad when Modbus is down?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
308
AndrewScott
Admiral AndrewScott
98
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Anonymous user
Not applicable

Posted: ‎2019-12-11 05:51 AM . Last Modified: ‎2023-05-03 12:19 AM

0 Likes
14
5746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-11 05:51 AM . Last Modified: ‎2023-05-03 12:19 AM

How to set quality to bad when Modbus is down?

Hello everyone.

 

I've noticed that my ClearSCADA (80.6914) don't write to archive value with bad qulity for modbus points when connection to modbus server is lost. 

 

Here I shut down modbus server and point has quality  "Last Known Value".

2019-12-11_15-34-03.png

 

And here it started again.

2019-12-11_15-42-25.png

 

But in Historic List there are only Good values.

2019-12-11_15-44-09.png

 

It's a problem. I need to see bad quality values in archive when connection was lost.

As a solution I can make for every modbus point a couple Internal point and a logic that will copy values with quality. This Logic will link quality in internal Point to Modbus Scaner Status. But maybe there is more easy way?

 

Also I've found interesting option in Advanced Modbus - Direct Outstation - Log Historic Value On Communication Failure. It sounds as that I need. I just can't make this advanced thing work.

Labels
  • Labels:
  • Drivers
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2019-12-12 02:17 AM

In response to Anonymous user
0 Likes
6
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 02:17 AM

The channel is out of service in "am.sde", unlike the screenshot above.

Once I put the channel into service this configuration works for me.

 

Given that the channel state is showing "Disconnected" it looks like the Advanced Modbus driver isn't actually running. You can check if the driver is running from the "General \ Modules" page of the Server Status tool on the main server, as well as starting and stopping the driver.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-12-11 06:33 AM

0 Likes
13
5740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-11 06:33 AM

The general principles of Remote SCADA (unwritten!) are that historic data should only be logged if it came from the device (and the quality reflects what the device's opinion of the signal was - e.g. if it was from a connected instrument and the instrument failed).

 

However, the Advanced drivers support adding single historic values when devices fail. I do recommend you use Advanced drivers when available for the protocol you want for all sorts of reasons. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-11 07:16 AM

In response to sbeadle
0 Likes
12
5737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-11 07:16 AM

Oh, then I just need some help with Advanced.

 

I have a simple modbus slave simulator that runs on my local computer just for test. 

 

2019-12-11_17-54-37.png

 

With simple modbus driver i see it without any troubles. So I need to connect to it with advanced. As help says it means link Dircet Channel - Direct Outstation Set - Direct Outstation - Point.

 

1. My Direct Channel settings

2019-12-11_17-52-37.png

 

2019-12-11_17-53-46.png

2019-12-11_17-56-33.png

 

2019-12-11_17-57-38.png

 

2. My Direct Outstation Set settings

2019-12-11_17-58-55.png

 

2019-12-11_17-59-20.png

 

3. My Generic Direct Outstation settings

2019-12-11_18-00-39.png2019-12-11_18-01-34.png

 

Direct and PSTN - all checkboxes are off.

2019-12-11_18-03-31.png

 

4. And finally Generic Analog Input Point

 

2019-12-11_18-08-24.png

 

 So that I have now.

 

2019-12-11_18-06-16.png

2019-12-11_18-09-23.png

 

2019-12-11_18-10-09.png

 

2019-12-11_18-11-11.png

 

I just can't understand what's wrong. For example here is config for Simple Modbus that works (when InService is on).

 

1. Scaner

2019-12-11_18-13-10.png

 

2019-12-11_18-14-33.png

 

2. Analog Point

2019-12-11_18-15-32.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2019-12-11 10:02 AM . Last Modified: ‎2019-12-11 11:35 AM

In response to Anonymous user
0 Likes
0
5728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-11 10:02 AM . Last Modified: ‎2019-12-11 11:35 AM

Your original issue, your historic list doesn't show any values recorded during the outage, so you will never see the "Last Known Value". The trend only updates connecting the last value, before the outage and the first value after the outage due to a setting. In the trend, you can change the point's "Trace Style" to Line, or Step Last. Step last will show the same flat line trace that you were seeing during the outage.

 

 

Unrelated. It is possible to pass the quality of a Modbus point to an internal point by connecting ModbusPointName.CurrentQuality to InternalPointName.PresetQuality via some logic. I do this regularly when I need to total together several flow rates or volumes but need to maintain the ability of the internal point to show the quality of the Modbus points to indicate when an outstation is out of communications where my Internal Total is displayed. 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2019-12-11 02:19 PM

In response to Anonymous user
0 Likes
10
5721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-11 02:19 PM

That all looks correct.

I even tried it on mine with a Modbus simulator.

You could try 127.0.0.1 instead of localhost

 

Make sure the Simple Modbus scanner is not in service at the same time. Maybe your simulator only supports one connection.

 

You can enable Comms Logging on the Channel and see if there is anything in the log to give you an answer to what the problem is.

 

Your Modbus simulator may also have logging. Mine does and I could see connection requests but then it closed the port. On the Channel, I forgot to set Modbus to TCP, it was still on RTU.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-11 11:05 PM

In response to geoffpatton
0 Likes
9
5710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-11 11:05 PM

Of course I switched off InService for Simple Modbus Scanner when tried Advanced. Modbus slave don't even see it's requests int it's log. I just don't understand why this thing doesn't work.

I keep in mind this model with AP (.CurrentQuality) -> IP (.PresetQuality) and it's the only way I see as solution. But my DB will double in size and there are more redundant work to do .

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-12-12 12:46 AM

In response to Anonymous user
0 Likes
8
5707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 12:46 AM

Would you mind posting an sde export of the config?

Have you contacted support?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-12 01:08 AM . Last Modified: ‎2019-12-12 01:10 AM

In response to sbeadle
0 Likes
7
5704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 01:08 AM . Last Modified: ‎2019-12-12 01:10 AM

No problem, these my two groups. am - Advanced Modbus, sm - Simple Modbus.

I though that problem is because my lack of understanding in reading help so didn't ask support still.

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2019-12-12 02:17 AM

In response to Anonymous user
0 Likes
6
5694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 02:17 AM

The channel is out of service in "am.sde", unlike the screenshot above.

Once I put the channel into service this configuration works for me.

 

Given that the channel state is showing "Disconnected" it looks like the Advanced Modbus driver isn't actually running. You can check if the driver is running from the "General \ Modules" page of the Server Status tool on the main server, as well as starting and stopping the driver.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-12-12 02:36 AM

In response to AndrewScott
0 Likes
5
5683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 02:36 AM

Thanks Andrew - you beat me to it!

Note that the analogue point had a Retrieval Interval of 'Continuous' so the driver will be kept busy polling - choose a suitable interval to match what you need.

You also do not have a Scan Group (Confidence Interval), which may be as required. This interval 'guarantees' update of value/time/quality at this interval. Be very careful to set this at the slowest rate needed, as on larger systems you can impair performance.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-12-12 02:44 AM

In response to sbeadle
0 Likes
0
5677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 02:44 AM

Example master and slave attached to this posting.

Attachments
Modbus Master Adv and Slave.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-12 02:48 AM

In response to sbeadle
0 Likes
3
5676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 02:48 AM

Yap, I switched InService On/Off in advanced and simple, so it could happens in the export I gave. 

But I have found. It's just....License....

As I understand, I need SCADAPackModbus License, that I don't have. 

Configuration above will work with appropriate license very well.

 

Thank you very much for help guys. I'm really appreciate it. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2019-12-12 03:21 AM

In response to Anonymous user
0 Likes
2
5669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 03:21 AM

If you're only using generic Modbus then you can just uninstall the unlicensed SCADAPack Modbus extension driver rather than obtaining a licence for it.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2019-12-12 05:30 AM

In response to AndrewScott
0 Likes
1
5663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 05:30 AM

I can confirm from my own system that even using Advanced Modbus, Generic Analog point with Scan Group (Confidence Interval) turned on, that no values are recorded in the Historic List while the Outstation is out of comms.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-12 09:46 PM

In response to Hardin4019
0 Likes
0
5612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-12 09:46 PM

Here is that I saw when cut off Modbus Slave and after enabled it.

 

изображение_viber_2019-12-12_13-42-40.jpg

 

Ih HL there are my national chracters but we see that one bad value is colored by violet.

 изображение_viber_2019-12-12_13-43-03.jpg

 

In Generic Direct Outstation enabled Log Historic Value on Communication Failure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of