How to send SMS from GeoSCADA to mobile phone

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • How to send SMS from GeoSCADA to mobile phone
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-07-10 02:25 PM

0 Likes
6
2285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-10 02:25 PM

How to send SMS from GeoSCADA to mobile phone

Hi

 

I am trying to find out how we can setup and run SMS sending service from scratch. I have tried different helps but not very helpful. 

I have found " SMS pager channel" and " SMS channel" but have no idea how to set it up. 

 

It will highly appreciated ,if anyone can help about this. 

 

Regards

Labels
  • Labels:
  • Drivers
  • Radio
  • RTU
  • SCADA
  • Telemetry
  • ViewX
  • Virtual ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-11 06:58 AM

1 Like
1
2279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 06:58 AM

Create a "Pager \ SMS Service" object for each service provider that you want to use (Vodafone, T-Mobile, EE, Three etc.).

Create a "Pager \ SMS Pager Channel" object for each modem and link the channel to an SMS service created earlier. The modems are used to send/receive SMS messages to/from the users of the associated SMS service.

Link your Geo SCADA user accounts to the SMS service(s) used by that user (see "Contact Information" tab on user form). Set the "Pager ID" to the user's mobile phone number (including the international dialling code, e.g. +44 in the UK).

 

You can now send messages to a user using the "Send Pager Message..." pick action on the user..

 

To send a message when an alarm occurs, create an "Alarm Redirection \ Pager Action" object and link to the user account (or user group or user roster) who will receive the messages. Link these pager alarm redirection actions to the objects (points, outstations etc.) who's alarms are to be sent (see "Redirection" tab on point/outstation form).

 

See Configuring Pager Devices in Geo SCADA Expert for more details.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-12 02:46 AM

1 Like
2
2226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-12 02:46 AM

If you're using an Ethernet modem then you need to specify the IP address and port number of the modem. These will be configurable. Consult the modem's documentation for details.

 

If you're using something like a USB modem connected to the GSE server then this will likely have a COM port (so use a Serial connection, not TCP/IP). Consult the modem's documentation for details. The Windows mode command can be used to list the available COM ports.

 

If you're trying to get the GSE server to access a remote modem connected to your laptop (or built-in to the laptop) then you will need additional software to provide remote access. The Port Server utility included with GSE can be used to do this in conjunction with a Remote Serial connection, providing the modem has a COM port on the laptop (as above).


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-18 02:13 AM

In response to Mehdi_Sajjadi
1 Like
0
2142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-18 02:13 AM

The "Pager Message" field on the "Pager Action" defines the SMS message that is sent. This can be fixed text or you can use trip sequences to insert properties of the alarm etc. see Trip Sequences Supported by Redirection Actions.

 

A pager action can be used as many times are required. You can also apply pager actions to groups which then apply to all of the items in the group. See Configure Alarm Redirections for an Item or Group.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-11 06:58 AM

1 Like
1
2280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 06:58 AM

Create a "Pager \ SMS Service" object for each service provider that you want to use (Vodafone, T-Mobile, EE, Three etc.).

Create a "Pager \ SMS Pager Channel" object for each modem and link the channel to an SMS service created earlier. The modems are used to send/receive SMS messages to/from the users of the associated SMS service.

Link your Geo SCADA user accounts to the SMS service(s) used by that user (see "Contact Information" tab on user form). Set the "Pager ID" to the user's mobile phone number (including the international dialling code, e.g. +44 in the UK).

 

You can now send messages to a user using the "Send Pager Message..." pick action on the user..

 

To send a message when an alarm occurs, create an "Alarm Redirection \ Pager Action" object and link to the user account (or user group or user roster) who will receive the messages. Link these pager alarm redirection actions to the objects (points, outstations etc.) who's alarms are to be sent (see "Redirection" tab on point/outstation form).

 

See Configuring Pager Devices in Geo SCADA Expert for more details.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-07-11 08:54 PM

In response to AndrewScott
0 Likes
0
2237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 08:54 PM

Dear Andrew

 

Thank you so much, as always you are my first savior 🙂

Just a quick question, I have done all settings, as GSM is connected through TCP/IP to SCADA, I think in SMS pager channel/Connection tab I need to setup up "Host address" , "Port" , also It is needed to set "Line Speed"  in Channel tab.

 

My setup is :

Line Speed : 10240000

Host Address: my laptop IP

Port : ??

 

Would you please let me know If I am on right path and what is correct Port number ?

 

I appreciate it

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-12 02:46 AM

1 Like
2
2227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-12 02:46 AM

If you're using an Ethernet modem then you need to specify the IP address and port number of the modem. These will be configurable. Consult the modem's documentation for details.

 

If you're using something like a USB modem connected to the GSE server then this will likely have a COM port (so use a Serial connection, not TCP/IP). Consult the modem's documentation for details. The Windows mode command can be used to list the available COM ports.

 

If you're trying to get the GSE server to access a remote modem connected to your laptop (or built-in to the laptop) then you will need additional software to provide remote access. The Port Server utility included with GSE can be used to do this in conjunction with a Remote Serial connection, providing the modem has a COM port on the laptop (as above).


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-07-17 05:13 PM

In response to AndrewScott
0 Likes
1
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-17 05:13 PM

Hi Andrew

 

I appreciate your kind support. Based on your advices and guidance, Pager  service setup and working with no issue.

 

Just a quick question, for sending automatic message to operator I have enabled "Redirection" on "binary Input point", as you can see in attached photo "Automatic SMS-1" . 

 To setup message body for operator it is needed to write a message in  "Pager message" box in "Pager Action" tab. 

 

Would you please confirm it ,if it is correct? and is it needed to create a new "Page Action" for every point that we want to send their status through SMS? 

 

Regards

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-18 02:13 AM

In response to Mehdi_Sajjadi
1 Like
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-18 02:13 AM

The "Pager Message" field on the "Pager Action" defines the SMS message that is sent. This can be fixed text or you can use trip sequences to insert properties of the alarm etc. see Trip Sequences Supported by Redirection Actions.

 

A pager action can be used as many times are required. You can also apply pager actions to groups which then apply to all of the items in the group. See Configure Alarm Redirections for an Item or Group.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-08-08 02:27 PM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-08 02:27 PM

Thank you so much, very helpful. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore