Geoscada historian export to 3rd party
Hi Experts
Is there any way to export data from Geoscada - Selected tags from the historian to a 3rd party historian (Panorama H2 in this case). I have seen some info on the link below but no documentation on how this is done:
https://github.com/GeoSCADA/TransferHistory
Also is there any way to access data from the database folder - historic folder?
Any help would be highly appreciated.
Thank you!
- Labels:
-
ViewX
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-20 01:58 AM
Common ways to do this are to pull with SQL/ODBC. Getting the arrangement of queries right to avoid performance issues would be important, so you will be unable to get fast throughput.
The database files are binary formatted and often write-locked so not a good way to get data out.
The samples on GitHub can be used to build a push interface and customised for your choice of target. Choose the sample most similar to your interface a work from there. It's a hybrid push/pull so performance is mid level.