GeoSCADA Expert Mobile application unknown error during connection

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSCADA Expert Mobile application unknown error during connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
115
BevanWeiss
Spock BevanWeiss
98
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Antonio_Sgalla
Crewman Antonio_Sgalla
Crewman

Posted: ‎2025-07-28 01:02 AM . Last Modified: ‎2025-08-28 03:45 AM

0 Likes
3
342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-28 01:02 AM . Last Modified: ‎2025-08-28 03:45 AM

GeoSCADA Expert Mobile application unknown error during connection

Good morning, I installed and licensed successfully the GeoSCADA Expert Mobile Server, but when I try to access it from my mobile app I get "Unknown Error" as in the following screeshot.

My device is authorized in the Mobile Server Configurator and when I read the IIS logs I can see it returns the "404 not found" error code.

Could you help me with my problem, please?

 

Mobile error 2.jpg

 

Labels
  • Labels:
  • ViewX
  • Tags:
  • connection
  • english
  • error
  • expert
  • geoscada
  • mobile
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-07-29 03:21 AM

0 Likes
1
321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-29 03:21 AM

Hi Antonio,

you may need help from the Support team here.

You are correct to check the IIS logs. An initial connection from a mobile device will look like:

 

2025-07-29 10:11:53 192.168.1.29 GET /mobile/service.svc/v1/admin/device/pin - 443 - <address> Dalvik/2.1.0+(Linux;+U;+Android+12;+SM-M315F+Build/SP1A.210812.016) - 200 0 0 126
2025-07-29 10:11:53 192.168.1.29 GET /mobile/service.svc/v1/admin/servers - 443 - <address> Dalvik/2.1.0+(Linux;+U;+Android+12;+SM-M315F+Build/SP1A.210812.016) - 200 0 0 13
2025-07-29 10:11:55 192.168.1.29 GET /mobile/service.svc/v1/LOCAL/token - 443 - <address> Dalvik/2.1.0+(Linux;+U;+Android+12;+SM-M315F+Build/SP1A.210812.016) - 200 0 0 507

 

You can use a web browser to check the web connection by using the URL:

https://<address/name>/mobile/service.svc/v1/admin/pin

This will return True.

 

Check that the MOBILECOMPANION service is running, and (in IIS config) that the web server attached to the port is 'ClearSCADAMobile'.

Reply

Link copied. Please paste this link to share this article on your social media post.

Antonio_Sgalla
Crewman Antonio_Sgalla
Crewman

Posted: ‎2025-08-04 01:03 AM

In response to sbeadle
0 Likes
0
286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-04 01:03 AM

Good morning!

When I connect to "https://<SERVER IP>/mobile/service.svc/v1/admin/pin" I get "Secure connection failed"

Antonio_Sgalla_0-1754291820693.png

I'm in contact with the Support Team, thank you.

Best regards,
Antonio.

   

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-08-05 01:37 AM

0 Likes
0
275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-05 01:37 AM

I'm sure they can help, but looks like a certificate issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.