Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Geo SCADA Expert OPC-XML DA Authentication

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Geo SCADA Expert OPC-XML DA Authentication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
BevanWeiss
BevanWeiss
Champion

Posted: ‎2021-04-01 08:33 PM . Last Modified: ‎2023-05-03 12:04 AM

0 Likes
3
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-01 08:33 PM . Last Modified: ‎2023-05-03 12:04 AM

Geo SCADA Expert OPC-XML DA Authentication

In a similar vein as per my SOAP authentication problem, I have a similar problem with OPC-XML DA.

 

I'm using the Advosol OPC-XML DA Test Client, and if 'Everyone' has full Read/Browse permissions, then I can happily issue Browse / Read requests and get all the data.

 

If I then remove permissions from 'Everyone' and try to use 'Basic Authentication' with username/password set as a valid username/password for full system access (domain left blank), then I'm again unable to Browse anything, and Reads come back with E_ACCESSDENIED (apart from on things related to Server / System Status).  I expect this is because the http://localhost/webservices/scx endpoint doesn't force any 401 authentication challenge (to which the basic authentication might be provided).

 

It also appeared that the webservices weren't bound on the IPv6 localhost ::1 address which might become an issue in the eventual migration to IPv6 in the SCADA space.

 

Is there a custom security mechanism used for Geo SCADA Expert and OPC-XML DA?

@AdamWoodland / @sbeadle  I suspect this is likely more a question for the two of you, unless this is a case of RTFM somewhere 😉


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
BevanWeiss
Champion

Posted: ‎2021-04-08 04:56 PM

In response to AdamWoodland
0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-08 04:56 PM

And the answer is.... using a standard OPC-XML client will be VERY difficult for this.

It currently requires the use of cookies.  Which are only available from the /logon endpoint.

So it will require a bespoke OPC-XML client (as far as I'm aware none of the clients out there will allow for a different endpoint to be specified with a custom POST body to get the cookies for authentication)...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
AdamWoodland
AdamWoodland Mentor
Mentor

Posted: ‎2021-04-06 02:36 PM

0 Likes
2
3048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 02:36 PM

From what I remember when I asked this question in the past, OPC-XML-DA standard doesn't define any authentication mechanism so whatever those fields do its not as per the standard and they should be left blank.

 

So yeah, it means if you want to use OPC-XML-DA against Geo SCADA you need to allow Guest/Everyone read access at least to the data.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
BevanWeiss
Champion

Posted: ‎2021-04-06 09:11 PM

In response to AdamWoodland
0 Likes
0
3044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 09:11 PM

The OPC-XML DA specification does mention

Please refer to OPC Security Custom Interface Standard for additional insight into security concepts.

Which is an entirely seperate document

http://advosol.com/OpcSpecs/OPC%20Security%201.00%20Specification.pdf

 

Which itself mentions options being either DCOM Security or OPC Security (since it was created for OPC-DA).

For OPC-XML then DCOM Security makes limited sense, so OPC Security would have been the ideal way.

 

Given the portability of OPC-XML, and the Geo SCADA Expert security model not being purely NT-Token based, it would have made sense to support the Private Credential security interface (vs the NT Credential security interface), by implementing the below interface

IOPCSecurityPrivate
HRESULT IsAvailablePriv([out] BOOL *pbAvailable);;
HRESULT Logon([in, string] LPCWSTR szUserID, [in, string] LPCWSTR szPassword);
HRESULT Logoff(void);

Which I believe would have been a 1:1 connection to the existing Geo SCADA Expert web client situation (i.e. Logon, Logoff, leveraging HTTPS transport encryption), and connections being tracked and 'stateful'.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
BevanWeiss
Champion

Posted: ‎2021-04-08 04:56 PM

In response to AdamWoodland
0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-08 04:56 PM

And the answer is.... using a standard OPC-XML client will be VERY difficult for this.

It currently requires the use of cookies.  Which are only available from the /logon endpoint.

So it will require a bespoke OPC-XML client (as far as I'm aware none of the clients out there will allow for a different endpoint to be specified with a custom POST body to get the cookies for authentication)...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore