Geo SCADA 2022 v85.8390 - OPC UA Client Connection to OPC UA Server

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Geo SCADA 2022 v85.8390 - OPC UA Client Connection to OPC UA Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Aundrea_LaTech
Ensign Aundrea_LaTech
Ensign

Posted: ‎2023-02-09 10:11 AM . Last Modified: ‎2023-05-02 11:48 PM

0 Likes
7
2832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-09 10:11 AM . Last Modified: ‎2023-05-02 11:48 PM

Geo SCADA 2022 v85.8390 - OPC UA Client Connection to OPC UA Server

 

I am using Geo SCADA Expert to connect to an OPC UA Server for the first time. 

I am using Unified Automation UAExpert OPC UA Client installed on the Geo SCADA Server machine to test also.

 

On 2 separate test scenarios, the UAExpert client is connecting to the server with no issues, and I have not been able to successfully browse nodes through the Analog Point object in Geo SCADA. I have the following error showing up in the OPCUA Driver Log:
07-FEB-2023 18:03:54.291 [14168] connectError called. clientConnectionId: 0, serviceType: OpenSecureChannel, error: BadHostUnknown, overridable: false

 

I am researching error "BadHostUnknown" and it seems to be a DNS Issue. 

 

In my OPC UA server object, I have the following settings for Server URL and Endpoint:

 

Aundrea_LaTech_0-1675966233913.png

 

 

 

 

The OPC UA Server is replacing the IP address with "Compact" when it serves up the endpoints. Somehow this is not an issue for the UAExpert client, but it is an issue for Geo SCADA OPC UA Client. 

 

On a completely separate network and system, the UAExpert Client is successfully browsing nodes on an OPC UA Server and Geo SCADA installed on the same machine is experiencing a timeout when we try to browse nodes.

 

I have run several tests with a Discovery Server object in my project or without. I have tried to manually enter the Node address on the tag... The error I am getting on the OPC UA Server object is "State - Failed (Connection Error API Reconnect)".

 

I am wondering if anyone is aware of extra steps that must be taken when using the Geo SCADA OPC UA Client driver as opposed to this UAExpert Client that connects to the OPC UA Servers quite easily.

 

Labels
  • Labels:
  • Drivers
  • Tags:
  • english
  • opc ua
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
CoryMelaleuca
Crewman CoryMelaleuca
Crewman

Posted: ‎2023-02-09 12:41 PM . Last Modified: ‎2023-02-09 12:41 PM

0 Likes
0
2819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-09 12:41 PM . Last Modified: ‎2023-02-09 12:41 PM

Following this thread hoping to see my own "Connection Error API Reconnect" and "BadTimeout" issues resolved as I can browse the node once the server is established, but once I create a point whether analog, digital, or string, I cannot browse any node addresses. I just get a blank box where normally tags should be populating, or an unspecified error that populates as seen in this screen shot.

Screenshot.JPG

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-02-15 02:02 AM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-15 02:02 AM

Please can you raise these issues with the support team and send .sde config and driver log files to them?

Use the email address or phone number details in the ViewX About box.

(As the Geo SCADA driver uses a Unified Automation library, it's odd that their own client connects OK).

Thank you. 

Reply

Link copied. Please paste this link to share this article on your social media post.

daddybigal
daddybigal
Cadet

Posted: ‎2023-04-13 04:40 AM

0 Likes
1
2579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-13 04:40 AM

any luck with this issue? 

I have a problem when connecting  GeoSCADA OPC UA client to customer’s OPC UA Server (Kepware). The problem is that when the Endpoint of OPC UA Server is not None – None, the GeoSCADA OPC UA Client driver failed to connect to the OPC UA Server. GeoSCADA OPC UA Client driver is not sending its certificate to the OPC UA Server to make it as trusted OPC UA client even that we have imported the certificate into GeoSCADA database.

 

We have manually copied the GeoSCADA OPC UA client certificate into the OPC UA Server and trust it but we got the following error in the GeoSCADA OPC UA client driver log file:

“Calling UaSession::UaClientSdk::UaSession::connect
Connecting to the following Endpoint: opc.tcp://10.10.31.23:4991/FactoryTalkLinxGateway2
connectError called. clientConnectionId: 0, serviceType: OpenSecureChannel, error: BadUnexpectedError, overridable: false
Connection status changed to ConnectionErrorApiReconnect”

 

GeoSCADA OPC UA Client driver connected successfully to the OPC UA Server only if the OPC UA Server Endpoint is set to None – None.

 we need to connect using (Sign-Basic 256)

any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

daddybigal
daddybigal
Cadet

Posted: ‎2023-04-13 04:46 AM

0 Likes
0
2573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-13 04:46 AM

any updates on this issue, im facing the same, did you contact shcneider support?

Reply

Link copied. Please paste this link to share this article on your social media post.

CoryMelaleuca
Crewman CoryMelaleuca
Crewman

Posted: ‎2023-04-13 07:21 AM

0 Likes
0
2559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-13 07:21 AM

I have an open support ticket. I have submitted log files and have not received any help or updates unfortunately. I am convinced they need to escalate to their development team so that we can do a live support session or something. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Aundrea_LaTech
Ensign Aundrea_LaTech
Ensign

Posted: ‎2023-04-14 12:44 PM

In response to daddybigal
0 Likes
0
2541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-14 12:44 PM

I was helping Cory with our OPC UA Connection. It looks like you have had success with Endpoint set to None at least. We haven't had any success... even with Endpoint set to None... it looks like you've gotten further than us.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-04-25 03:41 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-25 03:41 AM

Linking to Mark P's post which explains how to set up certificates:

https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/OPC-UA-Driver-Setting-Geo-SCADA-2021-Rel-Fe...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore