Generate alarm from quality tag

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Generate alarm from quality tag
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
vpartinov
Crewman vpartinov
Crewman

Posted: ‎2020-07-30 05:43 AM . Last Modified: ‎2023-05-03 12:12 AM

0 Likes
13
4355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-30 05:43 AM . Last Modified: ‎2023-05-03 12:12 AM

Generate alarm from quality tag

I am using DNP3 protocol. Is there a way to generate alarm if quality tag of analog input point value is bad? 

Labels
  • Labels:
  • DNP3
  • SCADA
  • ViewX
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-07-30 07:44 AM

0 Likes
0
4343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-30 07:44 AM

You could use a digital calculation point whose value is based on the quality of the DNP3 analog point, the expression would be something like:

 

IIF( "<DNPPoint>.CurrentQuality" < 192, 1, 0 )

 

where <DNP3Point> is the full name of the analog point.

 

This will set the digital point to state 0 if good quality otherwise state 1, and you can configure state 1 to be alarm.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-07-30 07:44 AM

0 Likes
0
4344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-30 07:44 AM

You could use a digital calculation point whose value is based on the quality of the DNP3 analog point, the expression would be something like:

 

IIF( "<DNPPoint>.CurrentQuality" < 192, 1, 0 )

 

where <DNP3Point> is the full name of the analog point.

 

This will set the digital point to state 0 if good quality otherwise state 1, and you can configure state 1 to be alarm.


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-30 05:50 PM

0 Likes
11
4337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-30 05:50 PM

As Andrew has said... if the quality as reported from the Outstation is bad, then you may need to use another calculation point (or logic to drive an internal point).

 

If however you're talking about bad quality in the sense of Overrange / Underrange.. then it's off the shelf 🙂

2020-07-31 10_43_11-ViewX.png

 

If you configure the AlarmType / AlarmSeverity for the FullScale / ZeroScale, and the input value goes beyond these, then you will get an alarm.

It sounds like the Invalid might do something also... but I've honestly never used this, and I'm not sure what it would do... the help provides this guidance for it:

Invalid—Use to specify whether Geo SCADA Expert generates an alarm or event whenever the point’s value is reported as invalid by the outstation. Use the fields associated with this state to define the properties should the analog to digital conversion process fail in the outstation.

 

So I would think that you should be able to get the alarming that you want directly from an appropriate configuration of the DNP3 Analog Point Properties (Overrange, Underrange and Invalid).

 

This likely won't apply for your situation, but might be interesting to know anyway.  You can associated a Time Profile against the High High / High / Low / Low Low alarm limits... allowing the trigger points for these alarms to be time dynamic (both for time of day, as well as day of week).  I think this is an amazing feature of GeoSCADA, and one that not enough people know about / use...

However... you can't associate such a Time Profile with Overrange / Underrange / Invalid limits.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

vpartinov
Crewman vpartinov
Crewman

Posted: ‎2020-07-30 11:51 PM . Last Modified: ‎2020-07-30 11:53 PM

In response to BevanWeiss
0 Likes
10
4330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-30 11:51 PM . Last Modified: ‎2020-07-30 11:53 PM

Thanks to all for the solutions. I have never thought that in Clearscada can't create custom alarms until now, I don't know why is that... 

 

The alarm limits is not something for my case because some of the points from the outstation are from conversation from modbus to DNP3 and when the modbus is off (sometimes happens because of external voltage is off or battery voltage is off) the RTU gets the last value with 'good' quality tag and until the modbus is on, the RTU sends that value together with the timestamp and quality tag 'ComsLost' (or 'ComsFail' or something like that). 

 

As Andrew has said the calculations points are a solution but it will increase the points a lot and the license...

 

I figured out that there is a point 'Serial Error' in the RTU and if the value is not null there will be the alarm. It will be only 1 point per RTU so this would be the solution for me.

 

Some thoughts on why can't create custom alarms.. ? 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-08-01 12:25 AM

In response to vpartinov
0 Likes
9
4314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-01 12:25 AM

Depending on what RTU you have you can potentially get the DNP3 quality to indicate that it's not good... then the Invalid item on the Analog Point could be configured for the alarm.

 

Creating 'custom alarms' would make it incredibly confusing.  The existing alarms relate directly to the object that they occur on, and hence it's sensible.

 

The GeoSCADA system really has quite a strong inheritance system.  So Alarms are not things that just float around in space, they are associated with a CAlarmObject, and hence configuration for those alarms occurs ON the CAlarmObject instance.

 

 

I think in this situation the best would be if in the RTU, when the Modbus communications failed, the point itself was marked as 'Offline'.  Then you could alarm on that based on the Invalid AlarmType/AlarmSeverity 🙂


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2020-08-01 02:35 PM

In response to BevanWeiss
0 Likes
2
4306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-01 02:35 PM

Assuming you could add a point to ClearSCADA/GeoSCADA that shows the status of the communications from the RTU to the device converting Modbus to DNP3.... Would it be possible to use the point and .PresetQuality to change the quality of all of the points also?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-08-01 05:24 PM

In response to Hardin4019
0 Likes
1
4300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-01 05:24 PM

@Hardin4019  I'm pretty sure PresetQuality, PresetTimestamp only apply to Internal Points.

I would very much expect that these properties would not apply for DNP3 points.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-08-03 02:09 AM

In response to BevanWeiss
0 Likes
0
4293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 02:09 AM

@BevanWeiss is correct, PresetQuality and PresetTimestamp are properties of internal points. For 'real' points the quality and timestamp are determined by the driver based on the data received from the outstation.


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

vpartinov
Crewman vpartinov
Crewman

Posted: ‎2020-08-03 05:29 AM . Last Modified: ‎2020-08-03 05:31 AM

In response to BevanWeiss
0 Likes
4
4287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 05:29 AM . Last Modified: ‎2020-08-03 05:31 AM

The RTU marks the quality as 'Comm Failure' when the Modbus communications failed. Then the quality is marked as 'Comm Failure' and the status is marked as 'Offline; Comms. Lost' in ClearSCADA historic list of the point. The Invalid Severity is set on Alarm.

 

And there is the problem, there is no alarm raised and also the point state is not marked as 'Invalid'. When does ClearSCADA mark a DNP3 point state as 'Invalid'?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-08-03 06:36 AM

In response to vpartinov
0 Likes
3
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 06:36 AM

The invalid state on DNP3 analog points is only used when the outstation sets the REFERENCE_ERR flag on the analog point (see IEEE 1815-2012 Table 11-5 for flag descriptions). The DNP3 object flags are shown in the various status fields in ClearSCADA, including the historic list and view status dialog. These flags are used to calculate the DNP3 point's OPC quality within ClearSCADA.

 

There is no built in feature to raise an alarm (or change point state) based on any of the other DNP3 object flags.


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-08-03 07:30 PM

In response to BevanWeiss
0 Likes
0
4271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 07:30 PM

You can create custom text alarms - ie they aren't associated with an object alarm state. Use the SetInterfaceAlarm method on CRootGroup.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-08-04 05:14 PM

In response to AndrewScott
0 Likes
2
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-04 05:14 PM

@AndrewScott That does seem like a very specific situation re: the REFERENCE_ERR flag being the only flag considered as 'Invalid' for the alarming.  I don't recall that being in the Help... perhaps this does need to be a bit more explicit.

 

I would have expected (and we know that I generally have Great Expectations) that an Invalid alarm would be raised if there was a ('Invalid') state reported from the DNP3 outstation for that point that wasn't captured elsewhere (e.g. Underrange and Overrange are captured, as is 'Local Overrride'..).

 

Perhaps we just need more fine grained control over alarms for different DNP3 reported point states.. which does sound a little horrible, since there are already quite a lot of alarm states around the E-series / x70 DNP3 points as is (I've never used any more than the 2 high/low alarm limits... is there anyone that does?)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-08-05 03:47 PM

In response to BevanWeiss
0 Likes
1
4252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-05 03:47 PM

I know of a certain large water customer that uses all eight (all four low and four high). Why though is a question I can't answer.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-08-06 06:11 AM

In response to AdamWoodland
0 Likes
0
4240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-06 06:11 AM

And don't forget the 18 limit alarm feature in GeoSCADA!! Just a click away on the Server Config.

And - the Summer/Winter limit selection per group too...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of