GPS Tracking

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GPS Tracking
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-03-09 12:02 PM . Last Modified: ‎2023-05-03 12:16 AM

1 Like
6
4224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-09 12:02 PM . Last Modified: ‎2023-05-03 12:16 AM

GPS Tracking

We see a mentioning in our ppts of the capability to do GPS tracking with the Geo SCADA.  The question is.. how.  So we see the objects/users have the location attribute, but what about a vehicle? If we have access to a vehicle fleet monitoring service provider with GPS systems, how do we connect it to SCADA?  Is this explained in the Geo SCADA help guide and I just missed it? Thank you for your help.

 

 

Labels
  • Labels:
  • SCADA
  • Telemetry
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-03-10 01:22 AM

1 Like
3
4213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-10 01:22 AM

Hi! Here's an introduction.

 

To show anything's location on a map it needs to have a Latitude and a Longitude. Usually to display this we use the pre-built database fields in the Aggregate 'CGISLocation'. And we need a way to feed the two Latitude and Longitude numbers into these fields.

 

If you wish to track an RTU, then the location should be available as two 'analogue' point values, and when they are read you need to push these values into the CGISLocation fields on an object (for example, the RTU object itself). I don't know what GPS hardware you have, and I hope other people can advise how to read from the GPS hardware and store that into registers.

 

Alternatively you might have locations for things coming from an external database or application. In this case you need to feed these also into the same CGISLocation fields.

 

In order to write into these location fields you need to alter the location type property on an object to 'Dynamic'. (See image).

Annotation 2020-03-10 081321.jpg

 

 

 

 

 

 

 

 

 

 

 

 

Then you need to write into the values. 1131 Logic can do this - and can run when new data values are available.

For example (not a complete example):

Annotation 2020-03-10 082139.jpg

I hope this helps.

Steve

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-03-10 01:22 AM

1 Like
3
4214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-10 01:22 AM

Hi! Here's an introduction.

 

To show anything's location on a map it needs to have a Latitude and a Longitude. Usually to display this we use the pre-built database fields in the Aggregate 'CGISLocation'. And we need a way to feed the two Latitude and Longitude numbers into these fields.

 

If you wish to track an RTU, then the location should be available as two 'analogue' point values, and when they are read you need to push these values into the CGISLocation fields on an object (for example, the RTU object itself). I don't know what GPS hardware you have, and I hope other people can advise how to read from the GPS hardware and store that into registers.

 

Alternatively you might have locations for things coming from an external database or application. In this case you need to feed these also into the same CGISLocation fields.

 

In order to write into these location fields you need to alter the location type property on an object to 'Dynamic'. (See image).

Annotation 2020-03-10 081321.jpg

 

 

 

 

 

 

 

 

 

 

 

 

Then you need to write into the values. 1131 Logic can do this - and can run when new data values are available.

For example (not a complete example):

Annotation 2020-03-10 082139.jpg

I hope this helps.

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

LorenR
Ensign LorenR Ensign
Ensign

Posted: ‎2020-03-12 12:42 PM

In response to sbeadle
0 Likes
2
4167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-12 12:42 PM

Hi @sbeadle 

 

I have fwd your response to our S.I. but I'm afraid it is still not clear enough for them to implement it.. So we have already located assets on the map the regular way using the Latitude and Longitude as you mentioned below, but we haven't been able to make the Dynamic location work, and even less to integrate the GPS vehicle fleet monitoring service to the SCADA.  We're stuck I believe in the how to bring/feed these values to the dynamic location of the object, and about the GPS vehicle fleet monitoring system,  what kind of object should even be used to connect that system to the SCADA. And I'm afraid I have no experience developing scripts to guide them. 

 

Steve, is there a place, a manual, anything with instructions that we could follow to make this work?

 

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-03-12 11:23 PM

In response to LorenR
1 Like
1
4161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-12 11:23 PM

There really isn't much difference between Static / Dynamic for the GeoLocation, other than where the Latitude/Longitude are stored (Static is in the Config stream, Dynamic is in the Data stream).

 

So, you need to get the Latitude and Longitude from your field into the SCADA.  How you do this is not a Schneider thing.  You could use a web service hook to get it from a cloud service, or read it as a string from a GPS capable GSM modem, or read it as two REAL values from somewhere... it doesn't matter.

 

Once you have that value, then as @sbeadle mentioned, you just need a piece of Logic, whether you do this as FBD, LAD or ST doesn't matter, but it should be triggered 'On Change' of the Latitude/Longitude from paragraph one (1).  Hence having the latitude/longitude as a Point is advised, since that makes the logic triggering easy.

 

If the SI is having problems breaking down this problem into the individual parts, and executing these, there are other SIs available which could perform this work 😉


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-03-13 01:28 AM

In response to BevanWeiss
1 Like
0
4159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-13 01:28 AM

This is less of a GPS problem and more of an integration problem.

Geo SCADA has lots of ways to get data values from external systems into the right place.

I think the S.I. needs to describe the source of data and understand how it can be read.

For example, is it in a SQL database which can be read by ODBC?

Or is there a web service which a program can poll?

Or in a file which can be opened and read at intervals?

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2023-12-01 09:03 AM

0 Likes
0
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-01 09:03 AM

Hello Steve, can you please show how the structure for the query is??

Reply

Link copied. Please paste this link to share this article on your social media post.

thomesjames
thomesjames
Cadet

Posted: ‎2024-06-27 04:35 AM

0 Likes
0
1711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-27 04:35 AM

Connecting a vehicle fleet monitoring service provider's GPS systems to Geo SCADA involves integrating the GPS data into the SCADA system. Typically, this integration requires establishing communication protocols or APIs between the GPS service provider's platform and Geo SCADA. You'll need to configure Geo SCADA to receive and process location data from the GPS systems, ensuring compatibility and data consistency. For detailed guidance, check the Geo SCADA help guide for specific instructions on setting up external data sources and integrating them seamlessly. This approach ensures efficient fleet management and real-time monitoring capabilities within your SCADA environment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.