Hi everyone,
I'm trying to connect a Schneider Electric M580 PLC to Geo SCADA using EtherNet/IP. The PLC is configured with a NOC module at IP address 192.168.0.88. I'm able to set up the outstation, but when I try to browse or manually enter a tag name (e.g., 25_FI_121B_EUHI), I get the following error:
"Tag Name Element '25_FI_121B_EUHI' is Invalid. Tag Name Element is allowed alphanumeric characters, colons and underscores. Must start with either an underscore or alphabetic character."
When I try to browse tags using the ellipsis (
...) button in Geo SCADA, I receive a timeout error:"This operation returned because the timeout period expired. (0X8001011F)"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-29 12:58 AM
The Geo SCADA Ethernet/IP driver is documented and tested against AB devices, not SE M580.
The timeout error is interesting - perhaps raise a support case with the logs?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-28 12:42 PM
Well if you have not done so already you can try changing the tag name. Your example starts with a 2 and a 2 is number not an underscore or alphabetic character.
I have only connected to Allen Bradley PLCs and sometimes it does not show all the tags using the browse, but I have not tried to figure out why.
I would would not be surprised that if there are any tags that do not match its format criteria then the browse will fail.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-29 12:58 AM
The Geo SCADA Ethernet/IP driver is documented and tested against AB devices, not SE M580.
The timeout error is interesting - perhaps raise a support case with the logs?