Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82177members
349772posts

Execute structured text program with pick param and pick type animation

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
Tanquen
Lt. Commander
Lt. Commander
0 Likes
2
1106

Execute structured text program with pick param and pick type animation

The current application has two checkboxes, one to disable the tags alarm with the '?Digital.Disable' and one to set a PLC bit for that alarm with the '?Control&Value="1"'. They have some level alarms that were four separate alarms that they now want combined so that was easy enough to add a calculation digital point and disable the four alarms. Now just the calculation digital point goes into alarm when any of the four are true and the checkbox just disables the new calculation digital point.

 

Now I'm trying to figure out how to make the one check box toggle the four PLC bits. Working with buttons I know you can't just have a pick action method set four values at once so I made a structured text program to look at one of the bits and if it's true make them all faults if it's false make them all true. 

 

It's easy enough to make the pick action method with the structured text object selected and then the method set to execute and it works but for the life of me I can't figure out how to get it to work with the pick param and pick type animation. I know there's an execute method in the schema so I must have the syntax or the spelling or something wrong but it never does anything and it's really frustrating because the pick action keeps getting setup and it's confusing as to which ones actually working. The pick param and the pick type that you've configured under animations or the pick action that also looks like it's set up. I'm using pick type 5 and I think that should work with the execute method. I did try the others 17 and 19 and 20 and whatever and none of those work and they only seem to work with VB. Also the example for 19 makes it look like you can just put a message box command with a string and have it work and their example doesn't work.

 

So this works in a pick animation:

SCX:////CLogicSTProgram/...Tags DNP.Bioxide.Calcium Nitrate Tank 6701.Level SP.Toggle Rdy Tags

Untitled.jpg

 

 

But this don't work in a pick param animation:

 

"SCX:////CLogicSTProgram/...Tags DNP.Bioxide.Calcium Nitrate Tank 6701.Level SP.Toggle Rdy Tags"+'?Execute'


Accepted Solutions
Hardin4019
Lieutenant
Lieutenant
1
1083

Re: Execute structured text program with pick param and pick type animation

Drop the SCX:////CLogicSTProgram/ and try again. I did a test with PickType 5 and PickParam ".PickActionTest.ObjectLink"+'?Execute' that executes a ST that toggles an internal point form 0 to 1 and back. Worked like a champ. 

See Answer In Context

2 Replies 2
Hardin4019
Lieutenant
Lieutenant
1
1084

Re: Execute structured text program with pick param and pick type animation

Drop the SCX:////CLogicSTProgram/ and try again. I did a test with PickType 5 and PickParam ".PickActionTest.ObjectLink"+'?Execute' that executes a ST that toggles an internal point form 0 to 1 and back. Worked like a champ. 

Tanquen
Lt. Commander
Lt. Commander
0 Likes
0
1073

Re: Execute structured text program with pick param and pick type animation

Thanks, I'm so confused as to the best way to go. Since I couldn't get that to work I ended up putting the check box inside the group with the rest of the tags and the structured text object. Now I just have to drag the checkbox onto the screen and it's already linked. I was trying to figure out a way to use parameters to have the checkbox on the screen and then drag the structure text object onto it. I think it's better having it already linked but now it's completely different than all the other check boxes. They sure don't make the syntax on any of the number of ways you can do stuff easy. I put the SCX prefix on there because it's on there in the pick action wizard so you would think it would be similar using the pick param. I was also missing the .objectlink.