Posted: 2022-10-19 07:59 AM . Last Modified: 2023-05-02 11:51 PM
I am attempting to set up multiple Ethernet IP outstations (AB logix processors) on a single IP address but at different slot locations. I've tried to set this up but can only get one Outstation to communicate at a time. I'm wondering if I am not setting this up correctly or if this functionality is impossible with GeoSCADA.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-19 08:11 AM
This sounds like a known issue (CSUP-12891) that was fixed in the May 2022 monthly release of Geo SCADA, see the release notes for more details.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-28 09:32 AM
Thanks for the reply.
I was able to finally upgrade to the release that claims to address this issue, but I am still unable to connect to multiple processors in different slots, via the same IP address. When I double-check the release notes it seems to indicate that the port number must be unique. Doesn't Ethernet IP only use a single port for TCP (44818)? How am I supposed to use a unique port? It seems that a better solution would have been to include the slot number as the unique identifier.
[CSUP-12891] EtherNet/IP driver: We now include the port number of the outstation's
address when checking for unique network addresses. This allows multiple EtherNet/IP
outstations to be configured with the same IP address, if their port numbers are unique.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-29 02:56 AM
The fix for CSUP-12891 changed the unique identifier from IP address and slot number to IP address, port number and slot number. The customer who reported that issue was using a router with port forwarding, which is why they had different ports.
In this same issue it was reported that they could only communicates with one outstation at a time and this was also fixed, but this isn't mentioned in the release notes.
I would suggest raising this issue with customer support.