G'day experts!
Config:
Geo SCADA version: 2020 September
OS: MS Server 2019
Is it a (seemingly undocumented) design feature of Geo SCADA that the list will not function correctly after Mimic 1 is embedded in Mimic 2?
When I view Mimic 1, the list works as intended. However, Mimic 2 shows the list as a white box and red cross like this:
Edit: for some reason I can't embed and image? here is an indicative sample (minus the "image" text):
https://askleo.askleomedia.com/wp-content/uploads/2013/07/image_not_found.png.webp
Please confirm this behavior is expected?
Thanks in advance,
vds
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-16 10:31 PM
Hi @Anonymous user ,
This is a known limitation of ClearSCADA / GeoSCADA unfortunately.
Embedded queries cannot be placed on embedded mimics and still work.
The work around is to find a way to place the embedded query on the top level overview.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-16 10:31 PM
Hi @Anonymous user ,
This is a known limitation of ClearSCADA / GeoSCADA unfortunately.
Embedded queries cannot be placed on embedded mimics and still work.
The work around is to find a way to place the embedded query on the top level overview.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-16 11:00 PM
Hi @BevanWeiss,
thanks for confirming... I wonder if it's a technical limitation or an artificial one to prevent abusing resources etc. Either way, I'm very sad 😢
cheers,
vds
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-17 01:24 PM
I suspect it's a bit of both.
There is a feature request in the Schneider system for this already, so you could get in contact with your local Tech Support and request another 'vote' on behalf of end-users/customers for this feature.
As embedded queries do have quite a performance impact, I can understand that it would be more difficult to handle them in regards to embedded mimics, and maintaining a consistent subscription list (since embedded mimics can be shared across instances etc, this would make the subscription situation trickier).