Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-14 07:01 PM
Hi,
Has anyone had a go at trying to get GeoSCADA to issue commands to set deadbands for DNP3 Analog Inputs on supported RTU/PLCs? I see in the DNP3 Specification, these are listed in the Object Group 34 variations 1-3.
thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 01:22 AM
Unfortunately the Geo SCADA DNP3 driver doesn't support group 34.
If you can use WITS-DNP3 version 3.0 then there is an equivalent significant change deadband feature (incremental record type 1019) which Geo SCADA supports.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 01:22 AM
Unfortunately the Geo SCADA DNP3 driver doesn't support group 34.
If you can use WITS-DNP3 version 3.0 then there is an equivalent significant change deadband feature (incremental record type 1019) which Geo SCADA supports.