DNP Object Group 34 Support
Hi,
Has anyone had a go at trying to get GeoSCADA to issue commands to set deadbands for DNP3 Analog Inputs on supported RTU/PLCs? I see in the DNP3 Specification, these are listed in the Object Group 34 variations 1-3.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-1701:22 AM
Unfortunately the Geo SCADA DNP3 driver doesn't support group 34.
If you can use WITS-DNP3 version 3.0 then there is an equivalent significant change deadband feature (incremental record type 1019) which Geo SCADA supports.