Crystal Reports Timeout on GEOSCADA

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Crystal Reports Timeout on GEOSCADA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
BGedco2022
Lt. Commander BGedco2022
Lt. Commander

Posted: ‎2022-03-20 01:37 AM . Last Modified: ‎2023-05-02 11:57 PM

0 Likes
3
2509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-20 01:37 AM . Last Modified: ‎2023-05-02 11:57 PM

Crystal Reports Timeout on GEOSCADA

Dear All,

 

Since yesterday, GEOSCADA failed to generate or export most of the crystal reports available on the system.

it takes the report generate or export request and after awhile (almost 10 minutes) a time out reported in the events journal .

 

 

appreciate any suggested solutions

 

best regards,

Labels
  • Labels:
  • Drivers
  • SCADA
  • Tags:
  • CrystalReports
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-20 04:23 PM

1 Like
1
2474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-20 04:23 PM

What's the full message in the event log, sometimes that can be specific as to the cause. You'll also need to check the Crystal Reports driver log file for errors.

 

What changed on the system the past few days? Something that might be seen as "irrelevant" such as setting a workstation name in the Configure Connections might cause some problems (although maybe not a 10 minute delay) as it only allows one client to connect.

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BGedco2022
Lt. Commander BGedco2022
Lt. Commander

Posted: ‎2022-04-02 11:06 PM

In response to AdamWoodland
0 Likes
0
2315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-02 11:06 PM

Thanlks @AdamWoodland 

 


@AdamWoodland wrote:

What's the full message in the event log, sometimes that can be specific as to the cause. You'll also need to check the Crystal Reports driver log file for errors.

 

What changed on the system the past few days? Something that might be seen as "irrelevant" such as setting a workstation name in the Configure Connections might cause some problems (although maybe not a 10 minute delay) as it only allows one client to connect.


We did look after what changes was made in the system.

One of the crystal reports was exported to disabled user (cause)

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-20 04:23 PM

1 Like
1
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-20 04:23 PM

What's the full message in the event log, sometimes that can be specific as to the cause. You'll also need to check the Crystal Reports driver log file for errors.

 

What changed on the system the past few days? Something that might be seen as "irrelevant" such as setting a workstation name in the Configure Connections might cause some problems (although maybe not a 10 minute delay) as it only allows one client to connect.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-03-20 04:25 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-20 04:25 PM

This seems more like something that you should raise with your local Tech Support.

You will need to collect both the DB logs and the Driver Logs (Crystal Reports) for these such events.

It would also be helpful if you had the Driver Logs for when things were working.

 

You should compare environments also.

Things obviously worked before, and now they don't work.  What has changed?

Have the Crystal Report queries been changed?

Has someone enabled anti-virus scanning of historical files / GeoSCADA Expert files which now causes performance issues with retrieving data?

Is the Crystal Reports driver been disabled? or otherwise prevented from doing things in a timely manner?


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BGedco2022
Lt. Commander BGedco2022
Lt. Commander

Posted: ‎2022-04-02 11:06 PM

In response to AdamWoodland
0 Likes
0
2316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-02 11:06 PM

Thanlks @AdamWoodland 

 


@AdamWoodland wrote:

What's the full message in the event log, sometimes that can be specific as to the cause. You'll also need to check the Crystal Reports driver log file for errors.

 

What changed on the system the past few days? Something that might be seen as "irrelevant" such as setting a workstation name in the Configure Connections might cause some problems (although maybe not a 10 minute delay) as it only allows one client to connect.


We did look after what changes was made in the system.

One of the crystal reports was exported to disabled user (cause)

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore