Configuring SNMP Point to process a specific trap

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
MarkPitout
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
6
2110

Configuring SNMP Point to process a specific trap

I need some advice on setting up an SNMP point to process a specific trap:

 

An SI of ours trying to set up Geo SCADA to receive SNMP traps from a third party VSWR monitor (from BirdTech), for a voice radio transmitter.

The specific trap we are trying to receive carries OID: 1.3.6.1.4.1.21581.1.5.0.2 as defined in the MIB file for the device.

  • We are able to poll for SNMP data from the device, on SNMP V2
  • We can receive the trap as a Generic trap, but the value displayed is simply “6”.
  • With WireShark we can see that an SNMP V2 trap is sent to the SCADA, with four Variables:
    • Variable 0: TimeTicks
    • Variable 1: OID with a value of 1.3.6.1.4.1.21581.1.5.0.2
    • Variable 2: The alarm message as an OctetString: for example: “TFR High Site Monitor,UHF 1,1.00,6.68,2.17,Alarm”
    • Variable 3: The IP address of the equipment sending the trap.

 

We have tried several permutations for setting up a SNMP String Point as a specific trap (tweaking, the Position, Location, Variable, and Specific Code fields), we’ve also selected and unselected the “Displayable as String” check box.

With all of our Specific Trap configurations, we’ve been unsuccessful at receiving the trap – the Process count for the point remains 0 and no value is displayed.

 

The help files give us generic descriptions for the fields that can be configured, but there is no example of how to set those fields for this particular scenario.

 

See attachments for details on the equipment and the trap we are trying to recieve.

GeoSCADA version is 2019 Build 81.7457

 

Any advice on how to configure the point to process this trap would be welcomed.

Attachments
Tags (1)

Accepted Solutions
MarkPitout
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Configuring SNMP Point to process a specific trap

Attached is the article I composed to address this topic.

See Answer In Context

Attachments
6 Replies 6
geoffpatton
Commander
Commander
0 Likes
0
2108

Re: Configuring SNMP Point to process a specific trap

I always find SNMP frustrating and not simple at all, mostly revolving around terrible or non existent mib files, and how to practically alarm off of traps and show an alarm has cleared.

 

I have not done much with SNMP in Geo/ClearSCADA, but for another SCADA platform we used Kepware to get the traps and then into a database. We, as in my coworker, did have to do some magic to keep from making duplicate entries. It holds the last X number (settable number) of traps it has received, and we would get up to 10 at a time from a device, but not always the same number so identifying new vs old was the issue.

Might be an option to purse if you just can't get it working in Geo/ClearSCADA,like you want.

Tags (1)
BevanWeiss
Spock
Spock
0 Likes
2
2083

Re: Configuring SNMP Point to process a specific trap

SNMP is a little confusing.

 

My suggestion is to use a separate SNMP Browser / Trap Agent to start with and confirm that you have the end device configuration all correct.

 

Wireshark is good for final verification, and comparison between conversations.  But you really want to start from a 'known good' configuration, and that is easiest to get working (from my experience) without ClearSCADA / Geo SCADA in the picture.

 

It is entirely possible that SNMP Traps themselves have some 'traps' since it's not a commonly used feature of ClearSCADA / Geo SCADA.  So you might want to prepare yourself for sending in a bug report (or two) around this functionality.

If you can get it working correctly with a third party SNMP Browser / Trap Agent, and then converting those settings across to ClearSCADA / Geo SCADA doesn't work, you could provide that information to your local Schneider Tech Support office. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
BevanWeiss
Spock
Spock
0 Likes
1
2010

Re: Configuring SNMP Point to process a specific trap

This doesn't sound like it's ClearSCADA / GeoSCADA related...  it sounds like you might be talking about either the WMI SNMP Server service, or the Windows SNMP Client service.  Neither of which will get SNMP Trap data into ClearSCADA / GeoSCADA (although the first can help to generate Trap data related to the Windows server itself... but there's normally other ways of doing that anyway.. like with the Performance Monitor driver).

 

Checking to see whether the Windows SNMP Client server has 'captured' the SNMP Trap port is worthwhile however.  Since if it grabs port 162 before ClearSCADA gets a chance to, then Traps to ClearSCADA won't work either..


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
geoffpatton
Commander
Commander
0 Likes
0
2004

Re: Configuring SNMP Point to process a specific trap

Bevan that message above yours looks like a spam account. one post and external links.

MarkPitout
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Configuring SNMP Point to process a specific trap

Hi All,

 

Schneider Electric Level 3 tech support came to my aid and helped me figure it out - the setup of the SNMP point in Geo SCADA to process specific traps is not very difficult, once you understand how it works. However, it isn't very obvious.

 

I'll be putting together a small how-to guide soon. I can post it here if you are interested.

 

Cheers,

Mark

MarkPitout
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Configuring SNMP Point to process a specific trap

Attached is the article I composed to address this topic.