Configurable/dynamic delay of alarm redirection?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Configurable/dynamic delay of alarm redirection?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
115
BevanWeiss
Spock BevanWeiss
98
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
AppSupport
Ensign AppSupport
Ensign

Posted: ‎2025-06-24 01:45 AM

0 Likes
2
436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-24 01:45 AM

Configurable/dynamic delay of alarm redirection?

Hi, we have a user requirement to allow an operator to dynamically enter a delay time for an alarm redirection... eg:

 

- Operator acknowledges alarm and enters a required time period

- Alarm reannunciates after specified time

 

Is there any way of passing the chosen time parameter into an alarm redirection as the delay period?

 

We have some configured redirections, and we use delays on some of these, but these are fixed whereas here the operator wants to choose the time period at the point of acknowledgement.

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-06-24 08:43 PM . Last Modified: ‎2025-06-24 08:44 PM

1 Like
1
422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-24 08:43 PM . Last Modified: ‎2025-06-24 08:44 PM

Not that I'm aware of.
It is possible to retrigger Alarm Redirections from Logic.  And the Alarm Redirection itself can be Logic... so what you can do is have something like the Alarm Redirection fire every 1 minute.  The Logic just looks to see if it should escalate.  If so, then it escalates it.  If not, then it just restarts the Alarm Redirection (resetting the timer, so in another 1 minute the logic will trigger again).

 

Notes: Be VERY careful what you set that time to.  Don't be smart and think 1s is a good value.  1 minute is an 'ok' value if you'll only have a few such alarms active.  If you'll have more than 60 alarms calling this logic, then it's possibly a bad plan.  You'd really want to do some performance testing.

The other option is to have the Logic such that it can manipulate the Configuration of the object to re-write the Alarm Redirection time (before re-triggering).  However, this writes to the Configuration Stream, has DB lock considerations, general IO performance considerations, and I generally don't like this idea (because once you've got Logic writing to Configuration fields like this it becomes a slippery slope).

 

The nicest might be to just have some set options for operators to assign, i.e. delay 5minutes, delay 15minutes, delay 30minutes, delay 1hr, delay 4hrs, delay 8hrs, delay 24hrs etc.. and then you could have Alarm Redirections for a very specific Alarm Severity range (i.e. AlarmDelayed5Min = 110-119, AlarmDelayed15Min = 120-129, AlarmDelayed30Min=130-139, AlarmDelayed1Hr = 140-149, etc...) and then the Logic just sets the Alarm Severity to the appropriate delay value (i.e. 141 for a 1Hr delay on a natural Severity 1 alarm), and then the Alarm Redirections for 140-149 will have a delay of 1hour and will escalate that delayed 141 severity up to 201 after 1 hour, where it will show up in the operator banner.  Having an operator enter a time at Acknowledgement doesn't quite work.. the alarm instance may or may not be active at this time.. and changing alarm severity (outside of Configuration Changes) only applies for a currently active alarm instance.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-06-24 08:43 PM . Last Modified: ‎2025-06-24 08:44 PM

1 Like
1
423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-24 08:43 PM . Last Modified: ‎2025-06-24 08:44 PM

Not that I'm aware of.
It is possible to retrigger Alarm Redirections from Logic.  And the Alarm Redirection itself can be Logic... so what you can do is have something like the Alarm Redirection fire every 1 minute.  The Logic just looks to see if it should escalate.  If so, then it escalates it.  If not, then it just restarts the Alarm Redirection (resetting the timer, so in another 1 minute the logic will trigger again).

 

Notes: Be VERY careful what you set that time to.  Don't be smart and think 1s is a good value.  1 minute is an 'ok' value if you'll only have a few such alarms active.  If you'll have more than 60 alarms calling this logic, then it's possibly a bad plan.  You'd really want to do some performance testing.

The other option is to have the Logic such that it can manipulate the Configuration of the object to re-write the Alarm Redirection time (before re-triggering).  However, this writes to the Configuration Stream, has DB lock considerations, general IO performance considerations, and I generally don't like this idea (because once you've got Logic writing to Configuration fields like this it becomes a slippery slope).

 

The nicest might be to just have some set options for operators to assign, i.e. delay 5minutes, delay 15minutes, delay 30minutes, delay 1hr, delay 4hrs, delay 8hrs, delay 24hrs etc.. and then you could have Alarm Redirections for a very specific Alarm Severity range (i.e. AlarmDelayed5Min = 110-119, AlarmDelayed15Min = 120-129, AlarmDelayed30Min=130-139, AlarmDelayed1Hr = 140-149, etc...) and then the Logic just sets the Alarm Severity to the appropriate delay value (i.e. 141 for a 1Hr delay on a natural Severity 1 alarm), and then the Alarm Redirections for 140-149 will have a delay of 1hour and will escalate that delayed 141 severity up to 201 after 1 hour, where it will show up in the operator banner.  Having an operator enter a time at Acknowledgement doesn't quite work.. the alarm instance may or may not be active at this time.. and changing alarm severity (outside of Configuration Changes) only applies for a currently active alarm instance.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

AppSupport
Ensign AppSupport
Ensign

Posted: ‎2025-06-26 02:39 AM

In response to BevanWeiss
0 Likes
0
398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-26 02:39 AM

Thanks Bevan, appreciate your response on this. Your comments are basically in-line with our investigations, which is why we haven't proceeded with any of the above methods. Really I was looking to confirm that I hadn't missed a simpler/easier approach, and from what you've said - I didn't 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore