Clarification on KB article about DNP3 AL timeouts between Geo SCADA and outstation

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Clarification on KB article about DNP3 AL timeouts between Geo SCADA and outstation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
rlao
Lt. Commander rlao
Lt. Commander

Posted: ‎2022-11-09 06:16 PM . Last Modified: ‎2023-05-02 11:51 PM

2 Likes
0
727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-09 06:16 PM . Last Modified: ‎2023-05-02 11:51 PM

Clarification on KB article about DNP3 AL timeouts between Geo SCADA and outstation

This KB article outlines how DNP3 comms issues can be caused if the AL timeouts between Geo SCADA and the outstation are not in sync.

 

A snippet of the article states that:

 

"The issue arises when ClearSCADA's AL timeout is set to be equal to or smaller than that in the outstation. The (old) DNP3 rules stated that an outstation will not respond to a new Read request if it has a pending response that requires a confirm."

 

However, the conclusion then states:

 

"To prevent this issue from occurring, the outstation AL timeout should be greater than the ClearSCADA AL timeout (usually by at least a couple of seconds)."

 

My questions are:

  • Shouldn't the outstation AL timeout be shorter than the Geo SCADA AL timeout by a couple of seconds, rather than longer? My understanding is that we want the outstation to time out first.
  • In a SCADAPack outstation object, what is the relevant field that this applies to? Is it the Master 1 configuration 'Application Layer Confirm (Event) Timeout' or the Application Layer 'Complete Fragment Timeout' or both that should be synced to the Geo SCADA AL timeout?
  • By a couple of seconds, will 1 second suffice? Should it be more? Or does it depend on the system?
Labels
  • Labels:
  • DNP3
  • RTU
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of