Changing a Group to Group Instance

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Changing a Group to Group Instance
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2021-07-23 08:41 AM . Last Modified: ‎2023-05-03 12:02 AM

0 Likes
2
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-23 08:41 AM . Last Modified: ‎2023-05-03 12:02 AM

Changing a Group to Group Instance

I did a quick search, and quickly came up empty. 

 

Situation:

 

I had a Group Instance of a meter template > that instance was converted to a standard Group / no longer an instance of any template. The point names, mimics, etc in this group still remain exactly the same as the original instance. > I want to convert the Group back a Group Instance of original template, or even a different template with the same point names and mimics.

 

Question:

 

Is there an easy way to do this without creating new points / ID's and or loosing history? Even if using a backup of the Group Instance was a possibility, I no longer have a backup that goes that far back.

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-07-23 08:57 PM

0 Likes
1
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-23 08:57 PM

Yeah, the 'waiter trick'... pulling out the table cloth and leaving the dishes.

 

You need to create a new Template.  This Template will be empty.

Then you create an instance of the Template.  Now you drag and drop all of your Group contents into the empty Template Instance in exactly the same structure as the Template that you eventually want to change it into.

 

Once it's all done, confirm the tag names and locations... because if you get this even slightly wrong, it will be lost data.

 

Once you've confirmed, then you go to the Template Instance, and Convert To... Instance of a Template (and pick the Template that you wanted it to become..)

If you did everything right, then the existing items will get pulled into the Template Instance which will now be an instance of the Template you wanted.

You could now delete the empty Template

 

There are a few traps to it.

a) in the past it has resulted in database inconsistencies (not sure if latest versions have this sorted... but you want to make sure Property Override values etc align).  Generally these issues won't cause normal execution errors.. but can become traps later if additional consistency checks are imposed by AVEVA, or if someone runs a Consistency Check on the production database (not recommended).

b) if you have the structure wrong etc, there's no warnings or internal checks.  You just end up losing points / history / etc from those items that didn't match (in naming / valid types).  This has caught me out on a hidden space at the end of an object name before... I think such spaces are no longer allowed... but you really want to double check the important stuff (maybe even phone a friend and get them to check too)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-07-23 08:57 PM

0 Likes
1
2014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-23 08:57 PM

Yeah, the 'waiter trick'... pulling out the table cloth and leaving the dishes.

 

You need to create a new Template.  This Template will be empty.

Then you create an instance of the Template.  Now you drag and drop all of your Group contents into the empty Template Instance in exactly the same structure as the Template that you eventually want to change it into.

 

Once it's all done, confirm the tag names and locations... because if you get this even slightly wrong, it will be lost data.

 

Once you've confirmed, then you go to the Template Instance, and Convert To... Instance of a Template (and pick the Template that you wanted it to become..)

If you did everything right, then the existing items will get pulled into the Template Instance which will now be an instance of the Template you wanted.

You could now delete the empty Template

 

There are a few traps to it.

a) in the past it has resulted in database inconsistencies (not sure if latest versions have this sorted... but you want to make sure Property Override values etc align).  Generally these issues won't cause normal execution errors.. but can become traps later if additional consistency checks are imposed by AVEVA, or if someone runs a Consistency Check on the production database (not recommended).

b) if you have the structure wrong etc, there's no warnings or internal checks.  You just end up losing points / history / etc from those items that didn't match (in naming / valid types).  This has caught me out on a hidden space at the end of an object name before... I think such spaces are no longer allowed... but you really want to double check the important stuff (maybe even phone a friend and get them to check too)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2021-07-25 01:21 PM

In response to BevanWeiss
0 Likes
0
2006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-25 01:21 PM

Thanks Bevan. This sounds like it should work just fine.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.