Calendar Redirection

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Calendar Redirection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Killultagh
Lieutenant JG Killultagh
Lieutenant JG

Posted: ‎2024-06-05 06:33 AM

0 Likes
6
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-05 06:33 AM

Calendar Redirection

I am looking to redirect alarms from a facility which is manned during the hours of Monday - Friday (8am to 4pm).

 

Using the calendar redirection functionality I am able to achieve the redirect during working hours however, come 4pm the alarm severity does not revert to its monitored state i.e. High.  I'm sure it is something as simple as using the correct 'Abort' setting.

 

The end-goal will be to revert the alarm to its monitored state if after 2 hours it remains in alarm even during the working day which may involve logic or VB I guess however, I am attempting to walk before crawling!

 

Has anyone experience in using the calendar functionality?  Our system is already using 1 hour redirection against comms failures and this works as expected.

Labels
  • Labels:
  • Scripting
  • Telemetry
  • ViewX
  • Virtual ViewX
  • WebX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-06-25 01:37 AM

0 Likes
1
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-25 01:37 AM

Thanks. What do these two redirections do?

sbeadle_0-1719304390447.png

I think the issue is a misunderstanding of what the redirection calendars do. A calendar states what will happen when an alarm state transition occurs. It does not make something happen when the calendar lists roll over to a new time/list.

I think you need a Logic program to force-redirect/restore alarms at your chosen time of 4pm.

(Assuming the answer to my query about what the redirections do is what I think they do!)

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-06-06 05:51 AM

0 Likes
2
1709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-06 05:51 AM

You write "the alarm severity does not revert to its monitored state i.e. High" - so are you modifying the alarm severity using the Change Priority Action? If so then the priority will not change back by the calendar - you will need another redirection or script to restore it.

Perhaps you don't need to change the priority to redirect?

Reply

Link copied. Please paste this link to share this article on your social media post.

Glenn
Glenn
Cadet

Posted: ‎2024-06-06 06:57 AM

In response to sbeadle
0 Likes
0
1699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-06 06:57 AM

Yes, we are currently using the Change Priority Action, for example to change the Alarm Severity from Medium to "Redirected Medium", which our Alarm Management Centre staff can't see, with the idea that if the cause of the alarm has not been resolved within 2 hours then the redirect will revert and the AMC staff will be notified with a Medium Alarm. Also that if the set time in which the site is manned elapses while an alarm is redirected, then it will also revert back to alarm.

 

Originally I tried an instant redirection to Redirected Medium, and a 2H delayed redirection back to Medium. However that just led to it once again being picked up by the first redirection, getting it caught in a loop.

 

Do you think there is a better way this could be done, if at all? I'm sure it could be done through script but we wanted to see if it could be accomplished with just using the calendar tools.

Reply

Link copied. Please paste this link to share this article on your social media post.

Killultagh
Lieutenant JG Killultagh
Lieutenant JG

Posted: ‎2024-06-06 07:06 AM

In response to sbeadle
0 Likes
0
1699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-06 07:06 AM

Steve

 

Yes that is correct, we are using the Alarm Redirection Change Priority Action to change to a severity filtered out of the Alarm Monitoring Centre's alarm banner which does work and is tried and trusted with RTU comms failures.  If the alarm clears the redirection is stopped.

 

In this instance with manned works we wish for the alarm severity to be changed to one which is filtered out of the Alarm Monitoring Centre's alarm banner during working hours Monday - Friday (8am-4pm).  Again this works similar to the comms failure alarms however upon the clock reaching 4pm the priority does not revert back to its configured alarm severity which can be annunciated on the alarm banner.

Reply

Link copied. Please paste this link to share this article on your social media post.

Killultagh
Lieutenant JG Killultagh
Lieutenant JG

Posted: ‎2024-06-24 03:29 AM

0 Likes
0
1555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 03:29 AM

Here are some screen shots to provide some further detail into the problem.  The redirection successfully applies as expected when an alarm is generated at source from Critical to Redirected Critical and be hidden from the Alarm Management Centre alarm banner with applied filters.  If the IO continues to be in alarm come the end of the day (in this case 16:00) it should redirect its alarm severity back to its configured severity (in this case Critical) to be actioned by the Alarm Management Centre.  The issue is that the redirection does not release when it is 16:00.  Any help would be appreciated.

 

1.jpg

 

2.jpg

 

3.jpg

 

4.jpg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-06-25 01:37 AM

0 Likes
1
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-25 01:37 AM

Thanks. What do these two redirections do?

sbeadle_0-1719304390447.png

I think the issue is a misunderstanding of what the redirection calendars do. A calendar states what will happen when an alarm state transition occurs. It does not make something happen when the calendar lists roll over to a new time/list.

I think you need a Logic program to force-redirect/restore alarms at your chosen time of 4pm.

(Assuming the answer to my query about what the redirections do is what I think they do!)

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Killultagh
Lieutenant JG Killultagh
Lieutenant JG

Posted: ‎2024-06-26 12:34 AM

In response to sbeadle
0 Likes
0
1517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 12:34 AM

Steve

 

Thanks for the response.  Yes it looks as if logic will be required to modify the severity at the time boundary if the signal remains in alarm.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore