Posted: 2023-03-03 12:43 AM . Last Modified: 2023-05-02 11:47 PM
Hello,
I have a problem in Geo SCADA. I calculated the daily average of a signal with using Calculation Tag. However the calculation date is different from recorded date. It records the average it got on the day it calculates, not the day it calculates, but the next day. I am sharing the screenshots of an example related to the situation I am dealing with below.
The data recorded in the database hourly for March 2 are as follows. The average of the data for that day is 16.5. But when I checked the Historic List of the Calculation Tag I created, I saw that the value 16.5 was saved on March 3, not March 2.
This is the Calculation Tag data. It recorded on 3rd March
The signal settings are as I have shared below. I couldn't see a setting to change the recording day. Can i change this? I am waiting for your answers.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-03 01:57 AM
The timestamp is controlled by the Output Timestamp setting. You're currently using "Time of Calculation" hence it gives the time that the expression was evaluated.
See Configure the Output Options for a Calculation Point for more details.