Hi guys,
is there a way to show ACK comment on embedded alarm list?
The goal is to show ack comment or filter alarms tha have been acknowledged with comment
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-14 02:24 AM
Extra columns can be added to the alarm list, see "Core Reference > Alarms > Configure Additional Alarm Columns > Add an Extra Alarm Column" in the help.
You will need to add an extra column for the "AlarmAcceptComment" attribute in each category, for example:
However, there isn't any option to filter alarm lists by comment.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-14 02:24 AM
Extra columns can be added to the alarm list, see "Core Reference > Alarms > Configure Additional Alarm Columns > Add an Extra Alarm Column" in the help.
You will need to add an extra column for the "AlarmAcceptComment" attribute in each category, for example:
However, there isn't any option to filter alarm lists by comment.