3rd party SNMP data

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • 3rd party SNMP data
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
DBurnside
Crewman DBurnside
Crewman

Posted: ‎2023-10-18 11:21 AM

0 Likes
8
2394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-18 11:21 AM

3rd party SNMP data

Hi is it possible to connect a 3rd party radio to display data on GeoSCADA via SNMP? It is current used with Schneider scanning radios for a management system.

 

We have previously used SNMP mibs to send data to a 3rd party management system but never tried to take SNMP data to be displayed on GeoSCADA itself.

Labels
  • Labels:
  • Telemetry
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-03-05 12:18 AM

1 Like
0
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-05 12:18 AM

Hi,

@BevanWeiss is correct, nothing dynamic. I suppose you can create some Logic to manipulate config, but it seems unnecessarily complicated. Geo SCADA is not an NMS, it's normally used to monitor a static network config which you know about when it's set up.

See Answer In Context

  • Tags:
  • solved
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2023-10-18 11:30 PM

0 Likes
0
2391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-18 11:30 PM

Yes, the GeoSCADA Expert SNMP driver supports 3rd party devices.  It's agnostic to the vendor.
You will just need to know the OIDs for the SNMP points you want to retrieve.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

mrazik
Crewman mrazik
Crewman

Posted: ‎2024-02-07 05:06 AM

0 Likes
3
2189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-07 05:06 AM

Hello, @BevanWeiss. Thanks. I can imagine that I can one-by-one add MANY OIDs for the 3rd party device and its own MIB... Is there any way to configure the "items/oids" automatically via importing the MIB file?

 

Also ... once created/generated such list of OIDs to be read, is there a way to store them as a "template" so that e.g. all devices within network XY can be queried by this list of OIDs? (I configure one template and it's used for all 3rd party devices within some group).

 

Thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2024-02-08 03:40 PM

In response to mrazik
0 Likes
2
2184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-08 03:40 PM

I would recommend not having hundreds of OID points scanned.  Just get 'important' ones.

I'm not sure that something like GeoSCADA is the right place to be polling for port status on 48 port switches, or similar.  That's definitely the realm of things like Solarwinds.

 

You can use the Bulk Edit Tool (I believe) to create SNMP Points.

Most longer term ClearSCADA/GeoSCADA integrators tend to use custom designed tools based on the Automation Interface (or the .NET API for newer developments).  I tend to use such custom tools rather than the Bulk Edit tool, hence I'm not 100% sure what functionality the Bulk Edit tool currently has.

 

You would create a Template containing the points, and then create instances of this Template.

If the template won't contain the SNMP Device itself (this may exist in a 'parent' template / group) then you probably want to use a Template Parameter to allow for the SNMP Device to be 'pushed down' to the various SNMP Points based on the Parameter Value assigned against the Template Instance.

 

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

mrazik
Crewman mrazik
Crewman

Posted: ‎2024-02-08 10:46 PM

In response to BevanWeiss
0 Likes
1
2177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-08 10:46 PM

Hi, thanks a lot.

 

I know Zabbix NMS and we use it a lot. SNMP and templates are OK there. But one customer has this GeoScada and wants to query values from the our devices via SNMP and I was thinking about the easiest way. One way is to really choose the most important ones and do them manually... Sure. I can completely understand that querying hundreds of values via GeoScada is not optimal and they should go for Solarwinds-Zabbix and similar.

 

One last question - for multiple values via SNMP we use "dynamic indexes" which must be discovered first. Is there any option for such behaviour? Because e.g. we can have one, or two, or 5 network interfaces. The OIDs are not fixed, but are dynamically created/deleted/changed over time. E.g. - https://www.zabbix.com/documentation/current/en/manual/config/items/itemtypes/snmp/dynamicindex.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2024-02-10 01:56 AM

In response to mrazik
0 Likes
0
2172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-10 01:56 AM

As far as I’m aware the full OID path for each point must be stored in the Config stream. So nothing dynamic available.

 

@sbeadle could possibly confirm this.

I’m not aware of any proposed (or easy) development to add dynamic OID config / discovery.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

mrazik
Crewman mrazik
Crewman

Posted: ‎2025-03-04 05:39 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-04 05:39 AM

Cheers, can @sbeadle let us know if anything dynamic is possible in GeoSCADA, as explained above? Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-03-05 12:18 AM

1 Like
0
1340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-05 12:18 AM

Hi,

@BevanWeiss is correct, nothing dynamic. I suppose you can create some Logic to manipulate config, but it seems unnecessarily complicated. Geo SCADA is not an NMS, it's normally used to monitor a static network config which you know about when it's set up.

  • Tags:
  • solved
Reply

Link copied. Please paste this link to share this article on your social media post.

mrazik
Crewman mrazik
Crewman

Posted: ‎2025-03-06 06:10 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-06 06:10 AM

Thank you! The thread can be closed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore