Softdpac portainer weidmüller plc docker

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • Softdpac portainer weidmüller plc docker
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
5
JeromePetit
Ensign JeromePetit Ensign
4
KarimBenameur
Ensign KarimBenameur Ensign
4
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Automation Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Solved
Oscrx
Crewman Oscrx
Crewman

Posted: ‎2023-01-30 11:15 PM . Last Modified: ‎2023-07-28 02:22 AM

0 Likes
9
3228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-30 11:15 PM . Last Modified: ‎2023-07-28 02:22 AM

Softdpac portainer weidmüller plc docker

Hello! So I was supposed to make softdpac run on a weidmüller plc via docker (portainer). However I have no clue on how I get this to work. Is there any guide out there like there is for Linux installation? 
I have made it work fine on my raspberry pi but there I can use a terminal and there are way more information online on how to make everything work.

I've tried a lot of different ways to make it work but no success yet. Any tips are welcome! 😄

extra question; how come I can only find my devices with usb - ethernet adapter but not straight ethernet-ethernet on automation expert? I can ping the devices with cmd with both ways but it doesnt show up on EAE when I only use ethernet.

Labels
  • Labels:
  • EcoStruxure Automation Expert
  • Hardware-Software decoupling
  • Topological Manager
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 04:57 AM

In response to Oscrx
1 Like
4
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 04:57 AM

Hi again, yes it is clearer now.

  1. You are referring to an older version of EAE i.e. 21.1. This installation method is still possible but is obsolete as it results in cyber security potential  issues.
  2. Soft dPAC pre-requisite is to have an open iPC with Linux (Debian/Ubuntu) / Docker / Docker compose / Python 3 where you can be admin.
    It seems that even if your iPC is running Linux it is a closed box and you are not able to install anything.
    I will suggest to use an IOT Box with an open OS instead.
  3. Another possibility in the future is to port our IEC61499 Runtime to this PLC using Universal Automation Organization. 


 

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 05:10 AM

In response to Oscrx
0 Likes
2
3172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:10 AM

As it is still possible to create unsecure Soft dPAC controllers using the python script...  I will say that you can do the same with Portainer by analyzing the script and reproducing each action with same parameters used in the script.

It is a long way to go &  it will not be officially supported. 

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 9
KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 01:56 AM . Last Modified: ‎2023-01-31 01:58 AM

0 Likes
8
3190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 01:56 AM . Last Modified: ‎2023-01-31 01:58 AM

Hello !

Portainer is not supposed to be used to create Soft dPAC controllers.

Please specify which version of Ecostruxure Automation Expert you are using.


Depending on your version, the only way to create a Soft dPAC controller is  from Ecostuxure Automation Expert / Physical Devices Editor.
It is for cyber security reasons as only authorized users can log to a Soft dPAC controller.

There was a python script that you can still  use but it will not be a secured Soft dPAC controller. 

 

Portainer can be used later to inspect or do some clean up if necessary.

 

As for you last question if you mean by "find" a discovery only the host can be discovered i.e.  your PI4 and not individual Soft dPAC unless they were created by script and that is not recommended.

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Oscrx
Crewman Oscrx
Crewman

Posted: ‎2023-01-31 02:43 AM

In response to KarimBenameur
0 Likes
7
3186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 02:43 AM

Hello!
Thank you for the reply!

I am using EAE v22.0.22181.16. On my weidmuller plc (uc20-wl2000-ac) I cant really use a terminal since the config is webbased so docker (portainer that is the preinstalled app) is the only way I can configure it if I am not mistaken.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 03:14 AM

In response to Oscrx
0 Likes
6
3183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 03:14 AM

Hi again,

Only way to create  is in EAE on Physical Device View :

  • add a server
  • Select Server port & on property enter your iPC IP adress. Please check that you iPC is reachable
  • select the server (not the port)
  • On contextual menu Manage Soft dPAC / Activate services
    you will notice a docker logo on server
  • On contextual menu Manage Soft dPAC / Activate services you will notice new items 
  • On the tool bar click on start monitoring
  • If you IPC is well configured you will be able to configure the security on the menu and a green shield will appears. Check the user manual for first user/password when required.
  • Now you can create your Soft dPAC controllers on same menu.

... And then you have to configure your Soft dPAC controller.

 

Point of attention :
IP adress must be on same subnet or reachable. Beware of any firewall that block the communication. will prevent you to deploy your application.

 

Now the need you are expressing is not covered.

If you explain in detail what are your need I can create an enhancement i.e. for instance "have a web interface to manage  secured Soft dPAC without EAE "

 

 

 

 
 

 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Oscrx
Crewman Oscrx
Crewman

Posted: ‎2023-01-31 04:40 AM

In response to KarimBenameur
0 Likes
5
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 04:40 AM

Hmm I think I've explained my issue poorly 😄 

So to explain it more clearly, our entire setup is a Raspberry Pi 3b+ as the "master" in this config and then a weidmüller plc uc20-wl2000-ac and a m251 TM251MDESE as "slaves" and all will communicate via modbus to raspberry pi. So what I want to do is to create a softdpac on my weidmüller plc just like I did on my RasPi, 
https://www.youtube.com/watch?v=ybzslvYVuZ8 - for reference on how I did it on Ras pi. Now I want to do this exact thing on my weidmüller plc also and I cant do it from the console since the only thing I can do is use weidmüllers webbased interface to configure.

I hope this makes it more clear. I might also be completely understanding it wrong 🙂

Sorry for being unclear

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 04:57 AM

In response to Oscrx
1 Like
4
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 04:57 AM

Hi again, yes it is clearer now.

  1. You are referring to an older version of EAE i.e. 21.1. This installation method is still possible but is obsolete as it results in cyber security potential  issues.
  2. Soft dPAC pre-requisite is to have an open iPC with Linux (Debian/Ubuntu) / Docker / Docker compose / Python 3 where you can be admin.
    It seems that even if your iPC is running Linux it is a closed box and you are not able to install anything.
    I will suggest to use an IOT Box with an open OS instead.
  3. Another possibility in the future is to port our IEC61499 Runtime to this PLC using Universal Automation Organization. 


 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Oscrx
Crewman Oscrx
Crewman

Posted: ‎2023-01-31 05:03 AM

In response to KarimBenameur
0 Likes
3
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:03 AM

Okay I understand now.

However there is an application on the OS already that is called "portainer" (docker) and from there I can run containers, however I suppose this doesnt work even tho I upload the correct images?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 05:10 AM

In response to Oscrx
0 Likes
2
3173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:10 AM

As it is still possible to create unsecure Soft dPAC controllers using the python script...  I will say that you can do the same with Portainer by analyzing the script and reproducing each action with same parameters used in the script.

It is a long way to go &  it will not be officially supported. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Oscrx
Crewman Oscrx
Crewman

Posted: ‎2023-01-31 05:15 AM

In response to KarimBenameur
0 Likes
1
3171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:15 AM

Okay thank you for all these answers! I understand it more clearly now. I presume that there is no document anywhere on how to do this "unofficial" way on portainer?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2023-01-31 05:51 AM

In response to Oscrx
0 Likes
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:51 AM

You are correct, there is no official document on how to do this "unofficial" way on portainer 🙂

You have to analyze mainly install.py & startSoftdPAC.sh. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now