Hi everybody.
We are using EAE ver. 24.0 and Standard.OPCUAClient (Version 24.0.0.4) library is referenced in our solution.
In the Properties pad of M580 dPAC, we could not find OPC UA Stack Confoguration as shown by below snapshot.
Is there something that we missed out? Please help. Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 11:19 PM
Hi @Eyanto ,
You will need to enable Advanced user level in the Buildtime settings to see these parameters.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 11:19 PM
Hi @Eyanto ,
You will need to enable Advanced user level in the Buildtime settings to see these parameters.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.