Hi, I have trouble to make formula from analog input data that i poll. For example, the value of AI1 is 33000. I want to divided the value by 1000. I want to make formula like this :
33000 / 1000 =
can somebody help me show the solution?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-16 08:45 PM
Hi Aliffdani,
There are two options to implement this formula: you can either use the Div block directly to calculate the value, or you can write the division formula in the basic block as Out: IN1/IN2. Attached the snaps for your reference.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-16 08:45 PM
Hi Aliffdani,
There are two options to implement this formula: you can either use the Div block directly to calculate the value, or you can write the division formula in the basic block as Out: IN1/IN2. Attached the snaps for your reference.