About bus cycle time and analog input sampling period

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • About bus cycle time and analog input sampling period
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
6
KarimBenameur
Ensign KarimBenameur Ensign
4
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Automation Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Start a Topic
Solved
kak
Crewman kak
Crewman

Posted: ‎2024-02-18 12:32 AM

0 Likes
4
1725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-18 12:32 AM

About bus cycle time and analog input sampling period

Hi experts,

I'm new to PLC programming so I need your help..

 

Now I have one M251 dPAC, DI, DO and AI module each. So I want to know analog input sampling rate in PLC.  AI module's sampling rate is 1ms (It seems not to be changed) and TM3 busCycleTime is 50ms. Analog input type is set to VTQREAL type, I can watch analog value change by time value. 

 

When I set busCycleTime to 50ms, It seems like analog value changed about 250ms cycle. And When I set busCycleTime to 200ms, It seems like analog value changed about 1s cycle. Why analog input value updates 5 times longer than busCycleTime? I can't understand this..

 

Please anyone explain this and provide any documents or references about this.

Labels
  • Labels:
  • EcoStruxure Automation Expert
  • Tags:
  • busCycleTime
  • english
  • sampling rate
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mohamedriswan
Ensign mohamedriswan Ensign
Ensign

Posted: ‎2024-02-21 11:05 PM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-21 11:05 PM

Hi Kak,

1)The frequency of the modulo event is at a maximum 1 every 5ms.

2)The occurrence every 5ms may be related to the conversion time of the AI module, as this time interval might be necessary for the module to process the signal. This relationship could be a factor in ensuring accurate and timely data acquisition.

3)Yes, the AI Module that you are using has having 1ms sampling rate, we can't change it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
mohamedriswan
Ensign mohamedriswan Ensign
Ensign

Posted: ‎2024-02-19 04:17 AM

0 Likes
0
1720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-19 04:17 AM

Hi Kak,

Regarding the bus cycle time 

When the bus cycle time is set to 50 ms, the maximum frequency of the modulo event, occurring every 5 ms, results in a value change cycle of 250 ms.
 
Regarding the AI module Sampling rate change.

You can adjust the sampling rate of the AI by accessing the AI module properties and switching the type from "Not used" to your desired parameter (e.g., voltage or current). This action will reveal a drop-down list, allowing you to set the sampling rate to either 1 ms or 10 ms.

mohamedriswan_1-1708344852688.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

kak
Crewman kak
Crewman

Posted: ‎2024-02-21 07:32 AM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-21 07:32 AM

Thank you for your answer, @mohamedriswan 

But I still can't understand it. What is the maximum frequency of the modulo event? And why is that occuring every 5ms? Is that related to conversion time of AI module? Can you tell me more detail?

 

And about AI module's sampling rate, maybe TM3AI2H module I'm using can't change sampling rate. Or maybe I'm missing something. 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

mohamedriswan
Ensign mohamedriswan Ensign
Ensign

Posted: ‎2024-02-21 11:05 PM

0 Likes
0
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-21 11:05 PM

Hi Kak,

1)The frequency of the modulo event is at a maximum 1 every 5ms.

2)The occurrence every 5ms may be related to the conversion time of the AI module, as this time interval might be necessary for the module to process the signal. This relationship could be a factor in ensuring accurate and timely data acquisition.

3)Yes, the AI Module that you are using has having 1ms sampling rate, we can't change it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Eric_Coudurier
Lt. Commander Eric_Coudurier Lt. Commander
Lt. Commander

Posted: ‎2025-01-16 02:37 AM

0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-16 02:37 AM

Perhaps it is a little bit too late to answer this question, but better late than never, and the answer may be of interest to others.
In fact, the module's hardware CAT includes an indication factor that triggers information based on a bus cycle number, which is fixed at 5 and cannot be modified. The value is therefore updated every 5 cycles, i.e. 250ms for a 50 ms cycle (5 x 50 ms).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore