Posted: 2025-01-08 01:57 AM
Hi, currently i am struggling to synchronize the time and date in EAE that connect M251 Dpac with my PC (Windows 11). For right now, if there is alarm triggered, the date displayed is 1/16/2020. Hope somebody can help me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-09 12:19 AM
Hello,
If you use EAE from 24.0, in the Physical Device Tab (Topology), you can right click your device, then select "Set Current Date & Time" to open the date time dialog.
If you use EAE prior to 24.0, you can use the NTP capabilities of the device. You can configure them in the device Properties in Logical Device Tab. Don't forget to deploy the Device Configuration.
Also, for NTP changes to be considered, the device need to be rebooted :
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-09 12:19 AM
Hello,
If you use EAE from 24.0, in the Physical Device Tab (Topology), you can right click your device, then select "Set Current Date & Time" to open the date time dialog.
If you use EAE prior to 24.0, you can use the NTP capabilities of the device. You can configure them in the device Properties in Logical Device Tab. Don't forget to deploy the Device Configuration.
Also, for NTP changes to be considered, the device need to be rebooted :
Best Regards