EcoStruxure Automation Expert / IEC 61499 Forum
Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-07-11 02:50 AM . Last Modified: ‎2023-07-28 02:21 AM
Any migration project for Modicon or non Modicon exisitng PLC into EAE, what is the minimum BUS Cycle supported in V23.0 for below:
1. SoftdPAC windows
2. SoftdPAC Linux
3. M580dPAC
4. M251dPAC
5. M262dPAC
Pls provide any supporting document or references
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-07-12 05:30 AM
Hi Anandbpillai,
what kind of information are you looking for ?
I suppose you are requesting Bus Master minimum bus cycle information ?
It will depends on the Bus Master i.e. Modbus, EIP, TM3, XBUS etc
And the DPAC ie Soft dPAC, M580d etc
For Soft dPAC Linux Docker we did some test with 10 ms with minimal jitter. Going under 5 ms is feasible but with more jitter. Beware that the test have been done on Harmony P6 (I5/I7) Ubuntu 20.04 and low latency patch. We expect to have better result (under 2 ms) with PREEMPT_RT that will bring almost real time performance to LINUX.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-07-12 05:30 AM
Hi Anandbpillai,
what kind of information are you looking for ?
I suppose you are requesting Bus Master minimum bus cycle information ?
It will depends on the Bus Master i.e. Modbus, EIP, TM3, XBUS etc
And the DPAC ie Soft dPAC, M580d etc
For Soft dPAC Linux Docker we did some test with 10 ms with minimal jitter. Going under 5 ms is feasible but with more jitter. Beware that the test have been done on Harmony P6 (I5/I7) Ubuntu 20.04 and low latency patch. We expect to have better result (under 2 ms) with PREEMPT_RT that will bring almost real time performance to LINUX.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-07-31 10:49 PM
Thanks @KarimBenameur do we have a consolidated list for Hardware dPAC's as reference pls.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.