Detection of communication loss between dPac's

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • Detection of communication loss between dPac's
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
5
JeromePetit
Ensign JeromePetit Ensign
4
KarimBenameur
Ensign KarimBenameur Ensign
4
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Automation Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Solved
BenoitDery
Crewman BenoitDery Crewman
Crewman

Posted: ‎2023-05-24 03:15 AM . Last Modified: ‎2023-07-28 02:21 AM

0 Likes
2
1283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-24 03:15 AM . Last Modified: ‎2023-07-28 02:21 AM

Detection of communication loss between dPac's

Hi experts,

What is the best practice to detect a communication loss between dPac's?

Example:

A DIG_IN mapped to a TM251dPac is linked the run command of a ATVdPac. When the Ethernet communication is lost I want the ATV to stop for security reasons.

Of course, I can use a time based trigger like E_CYCLE to check this, but I suppose there must be a better way.

Any suggestion would be much appreciated!

Labels
  • Labels:
  • Distributed Control
  • EcoStruxure Automation Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Richard
Lt. Commander Richard Lt. Commander
Lt. Commander

Posted: ‎2023-07-12 06:34 AM

1 Like
1
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-12 06:34 AM

Obviously here is no point checking just once, so E_CYCLE in the M251 dPAC is a good way to perform the check as this will trigger regular events to do the checking. Inside the ATV dPAC you can use something like E_DELAYR to check the received pulses - use the pulses to reset the delay timer. This way if the pulses stop, the delay timer will time out and can then trigger the logic to to stop the motor.

There are other ways but this is probable the simplest.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Richard
Lt. Commander Richard Lt. Commander
Lt. Commander

Posted: ‎2023-07-12 06:34 AM

1 Like
1
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-12 06:34 AM

Obviously here is no point checking just once, so E_CYCLE in the M251 dPAC is a good way to perform the check as this will trigger regular events to do the checking. Inside the ATV dPAC you can use something like E_DELAYR to check the received pulses - use the pulses to reset the delay timer. This way if the pulses stop, the delay timer will time out and can then trigger the logic to to stop the motor.

There are other ways but this is probable the simplest.

Reply

Link copied. Please paste this link to share this article on your social media post.

BenoitDery
Crewman BenoitDery Crewman
Crewman

Posted: ‎2023-07-24 05:56 AM

In response to Richard
0 Likes
0
1073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-24 05:56 AM

Thank you Richard! I guess I was hoping for a kind of automatic communication check. This was a question raised by a customer during a demo. I didn't include any communication check at the time, so the ATV fitted with ATV dPac stayed in its last state (running or not) when disconnection the network. This behaviour is of course something very important to be aware of.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of