Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.
Posted: 2023-04-17 08:16 PM . Last Modified: 2023-07-28 02:21 AM
I used the HMI or the EIP_EXPLICIT to send the messages. But they all do not get the response from the EIP server. There are no any cip packages in the wireshark.M580 dPAC with EAE 22.1. Has anyone tested it?
Posted: 2023-06-05 02:09 AM
Hi Shaojie,
M580d is not yet supporting EIP_EXPLICIT. It will come in a future version.
This was developed & tested only for Soft dPAC Docker Linux before even M580d supported EIP.
Can you test it with a Soft dPAC Docker Linux ?
Posted: 2023-04-18 12:43 AM
The Master EIP is a M580 DPAC
But What is the Slave?
Can you provide the reference?
Regards
Seb
Posted: 2023-04-18 04:51 AM
Hello, the information I have this EIP library it is only to internal tests. You could use these parameters to test:
Posted: 2023-04-18 06:26 PM
Hello Seb.
The slave is M580 BMEP584040.
I used the EIP tools to test that is OK.
Posted: 2023-04-18 07:40 PM
Hello ,Thank you for your information. I tested as you said, but failed.
The version of EAE is 22.1.
Hi Shaojie,
Posted: 2023-07-09 07:32 PM
OK.Thank you for your answer. I will try to test later.