Posted: 2021-10-12 08:51 PM
We had an incident where our Symmetra PX left load offline for a long time until a human being could get there to physically press the button to turn load on. This is not desireable. So I'd like to try to understand better, what happened.
Anyone want to give your take on the logs?
2021-10-11 11:03:20 System: Web user 'apc' logged in from 172.28.234.136.
2021-10-11 06:27:19 System: Network service started. IPv6 address 2604:1234:1234:1234:2C0:B7FF:FE52:D4B9 assigned by router.
2021-10-11 06:27:03 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:24:57 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:22:57 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:22:57 System: DNS Network Error, No route to host.
2021-10-11 06:22:51 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:22:51 UPS: A runtime alarm threshold violation exists.
2021-10-11 06:22:15 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:22:15 System: DNS Network Error, No route to host.
2021-10-11 06:22:09 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:22:09 UPS: The output power is now turned on.
2021-10-11 06:21:46 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:19:46 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:17:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:15:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:13:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:11:39 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:09:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:07:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:05:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:03:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 06:01:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:59:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:57:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:55:45 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:54:02 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:54:02 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:54:02 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:54:02 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:54:02 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:54:01 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:53:55 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:53:55 System: Email: Could not resolve 'SuperWonderfulHosting.net'.
2021-10-11 05:53:39 System: DNS Network Error, No route to host.
2021-10-11 05:53:38 System: DNS Network Error, No route to host.
2021-10-11 05:53:38 System: DNS Network Error, No route to host.
2021-10-11 05:53:35 UPS: The output power is turned off.
2021-10-11 05:53:35 UPS: Restored the local network management interface-to-UPS communication.
2021-10-11 05:53:27 System: Network service started. IPv6 address FE80::2C0:B7FF:FE52:D4B9 assigned by link-local autoconfiguration.
2021-10-11 05:53:22 System: Network service started. System IP is 172.28.234.220 from manually configured settings.
2021-10-11 05:53:06 System: Warmstart.
2021-10-11 05:51:45 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:49:45 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:47:45 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:45:45 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:43:54 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:43:41 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:43:28 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:43:15 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:43:02 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:42:49 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:42:36 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:42:22 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:42:09 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:41:56 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:41:53 UPS: A static bypass switch module fault no longer exists.
2021-10-11 05:41:52 UPS: A redundancy alarm threshold violation no longer exists.
2021-10-11 05:41:52 UPS: Redundancy returned.
2021-10-11 05:41:43 System: Email: Could not mail 'SuperWonderfulHosting.net'.
2021-10-11 05:41:37 UPS: The load no longer exceeds 100% of rated capacity.
2021-10-11 05:41:33 UPS: A static bypass switch module fault exists.
2021-10-11 05:41:32 UPS: A redundancy alarm threshold violation exists.
2021-10-11 05:41:32 UPS: Redundancy lost.
2021-10-11 05:41:32 UPS: The output power is turned off.
2021-10-11 05:41:32 UPS: The load exceeds 100% of rated capacity.
2021-10-11 05:41:30 UPS: A runtime alarm threshold violation no longer exists.
2021-10-11 04:50:57 UPS: No longer on battery power.
2021-10-11 04:50:55 UPS: On battery power in response to an input power problem.
2021-10-08 14:04:04 System: Detected an unauthorized user attempting to access the SNMP interface from 192.168.112.24
2021-10-08 14:04:04 System: Detected an unauthorized user attempting to access the SNMP interface from 192.168.112.24
2021-10-08 14:04:03 System: Detected an unauthorized user attempting to access the SNMP interface from 192.168.112.24
2021-10-08 14:04:03 System: Detected an unauthorized user attempting to access the SNMP interface from 192.168.112.24