Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Correcting false power values reported by Data Center Expert 7.2.6

DCO Troubleshooting

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • DCO
  • DCO Troubleshooting
  • Correcting false power values reported by Data Center Expert 7.2.6
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Resolving error collecting data
  • Reset password for the DCO client
  • How to install a genome only update
  • Downloading log files for troubleshooting
  • Correcting false power values reported by Data Cen...
  • Resolving error collecting data
  • Reset password for the DCO client
  • How to install a genome only update
  • Downloading log files for troubleshooting
  • Correcting false power values reported by Data Cen...

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to DCO Troubleshooting
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1106 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Correcting false power values reported by Data Center Expert 7.2.6

Picard EcoStruxureIT
‎2020-02-28 06:38 AM

Some rack-mount PDUs reporting power bank information to Data Center Expert 7.2.6 report wrong power and current data to Data Center Operation.

Known affected devices: AP8970, AP8888, AP8886, AP8881, AP8870, AP8862, AP8860, AP8853, AP8841, AP8832J, AP8831, AP8653, AP8632, AP8481, AP8441, AP7960, AP7853 ...

You will be able to see if your rack-mount PDUs are reporting incorrectly to DCO if you see a significant difference in a rack-mount PDU's total peak and average values per phase in DCO compared with DCE. This can be done by running a power sensor report of the device(s) in DCE for a time period of 30 days. This report will also show the average and peak values in the bottom table. These numbers can then be compared with the power data seen in the device properties in DCO.

This patch fixing the issue applies to DCE 7.2.6+:

DCE version
DCO version
Fix includes
7.2.6 and later Prior to 7.5 Power (kW)
7.2.6 and later 7.5 and later

Power (kW), Current (amps)

 

How do I know if my rack-mount PDUs might be reporting wrong power data to DCO?

  1. Click View Device Sensors on your device (rack-mount PDU) in DCE (e.g. AP8841).
  2. Look for Power - Bank 1 and Power - Bank 2.
  3. If the device has more than one power bank, it could be reporting wrong power data to DCO.

How do I apply the patch in DCE?   

  1. Make sure to have a recent backup in place of your running systems before applying the patch. 
  2. On the DCE server, open this URL: http://<DCE server ip>/nbc/status/SensorContexts.
    You must be logged in as an admin user.
    1. If you already have a previous version of this patch installed (prior to March 2016), remove the existing file: pduSensorUpdates.xml before proceeding.
  3. Download this file and upload it to the DCE server.
    The file has now been uploaded to the server and the patch is in place.

    Warning

    Uploading a malformed or corrupted file can totally mess up the system. 

The power values are now correctly transferred.

You can erase the false power data history and see the corrected values immediately* by deleting the external system (DCE) in DCO and adding it again. You will need to associate devices again in DCO. 

*Once the data has been gathered from DCE. It might take up to 1 day depending of number of devices.  

An alternative is waiting. Depending on the configuration in Data Center Operation (30 days by default), all the values will be corrected after the configured time period (30 days by default). In general, power data is stored for a year for report purposes so for reports, the data will take longer for the data to be fully corrected.

How do I know if my rack-mount PDUs might be reporting wrong power data to DCO?

  1. Click View Device Sensors on your device (rack-mount PDU) in DCE (e.g. AP8841).
  2. Look for Power - Bank 1 and Power - Bank 2.
  3. If the device has more than one power bank, it could be reporting wrong power data to DCO.

How do I apply the patch in DCE?   

  1. Make sure to have a recent backup in place of your running systems before applying the patch. 
  2. On the DCE server, open this URL: http://<DCE server ip>/nbc/status/SensorContexts.
    You must be logged in as an admin user.
    1. If you already have a previous version of this patch installed (prior to March 2016), remove the existing file: pduSensorUpdates.xml before proceeding.
  3. Download this file and upload it to the DCE server.
    The file has now been uploaded to the server and the patch is in place.

    Warning

    Uploading a malformed or corrupted file can totally mess up the system. 

The power values are now correctly transferred.

You can erase the false power data history and see the corrected values immediately* by deleting the external system (DCE) in DCO and adding it again. You will need to associate devices again in DCO. 

*Once the data has been gathered from DCE. It might take up to 1 day depending of number of devices.  

An alternative is waiting. Depending on the configuration in Data Center Operation (30 days by default), all the values will be corrected after the configured time period (30 days by default). In general, power data is stored for a year for report purposes so for reports, the data will take longer for the data to be fully corrected.

Attachments
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore