Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

"Trend Micro" Internet Security Suite causes communications issues with I/A Series R2/G3 (Niagara) software

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Trend Micro" Internet Security Suite causes communications issues with I/A Series R2/G3 (Niagara) software
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa116868
    sesa116868

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1492 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Trend Micro" Internet Security Suite causes communications issues with I/A Series R2/G3 (Niagara) software

Picard Product_Support
‎2018-09-09 08:50 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:48 PM

Issue

Various issues have been observed regarding the use of the I/A Series R2 WorkPlace Pro or I/A Series G3 Graphics access.  The following is a partial list of known issues caused by the Ethernet firewall built into the Trend Micro Internet Security Suite software:

  1. When attempting to install an R2 UNC license using the Admin Tool, the error "Unable to install license" is displayed.
  2. When attempting to connect to a UNC from the WorkPlace Pro tree, a "Cannot connect" error occurs.
  3. When attempting to access G3 graphics using the web browser, the user is unable to log into the station serving the graphics.
  4. When attempting to access R2 graphics using the web browser, the user is unable to display the graphics pages.
  5. When attempting to paste a .gif file to a UNC's remote library, WorkPlace Pro stops responding and must be closed with Windows Task Manager.
  6. When attempting to open a local station on the computer, using WorkPlace Pro, the Windows hourglass is displayed and the station never opens.

This list will be updated as additional issues are encountered.

Environment

Computer running "Trend Micro Internet Security Suite"

I/A Series R2 (Niagara) WorkPlace Pro software or attempting to use the computer to view I/A Series G3 (Niagara) graphics.

Cause

The I/A Series R2 software requires bi-directional communications over Ethernet port 80 unless the software has been user-configured to use a different Ethernet port.

The Trend Micro Internet Security Software Suite has a built-in firewall that blocks incoming access to Ethernet port 80.  The Trend Micro software does not allow this port to be unblocked because it considers web access to a "workstation class" computer as a security risk.

Resolution

The best solution to this issue is to use a different Internet Security software package on the computer that does not block the use of Ethernet port 80.  One approach is to use the "Server" version of Trend Micro Internet Security instead of the "Workstation" version.  Since port 80 is typically used on server systems as the IIS (Internet Information Services) access port, the Server version of the software does not block that port.

The alternate solution is to configure the I/A Series R2/G3 (Niagara) software to use a different Ethernet port for HTTP communications and Web services.  This change would need to be made in the R2 or G3 software installed on the computer as well as in every UNC or ENC being accessed from this computer.

See New installation of the I/A Series (Niagara) R2 WorkPlace Pro software cannot connect to existing UN... for more information.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5356
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore