"Tam32: Errors detected in file: filepath" when editing an imported Function Block program

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Tam32: Errors detected in file: filepath" when editing an imported Function Block program
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Jeff
    Jeff
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3218 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Tam32: Errors detected in file: filepath" when editing an imported Function Block program

Picard Product_Support
‎2018-09-11 07:50 AM

Issue

Tam32 error message appears when Editing a Function Block program. When editing the program, this error appears and elements are removed from the program.

Product Line

EcoStruxure Building Operation

Environment

  • Function Block/Menta Editor
  • Found when files created in an older version are used in a newer version of StruxureWare Building Operation.

Cause

This error message is literal. The line indicated as an error is a corrupted part of the function block program. You can determine this line by editing the file in a text editor such as Notepad++ and viewing the indicated line.

NOTE: These programs will continue to work as originally programmed.

Resolution

To identify the part of the program causing the error:

  1. Edit the Program that is in error
  2. When the message appears, note the line number and file before you press ok.
  3. Do not edit or attempt to save the program.
  4. Locate the file specified in the error message. In this case tempaut1
  5. The AppData folder is usually hidden, so you will need to manually type the file path into Windows Explorer
  6. Edit the file with notepad++ or another text editor
  7. Find the indicated line and determine what type of object is in error. In this example, the line indicated in the error was 116. It is a comment.

Method 1:

  1. Compare the error line to another other line of the same type in the document and correct any abnormalities. In this case, I removed an extra comma. If it is a Comment, note that @ = carriage return and should be left in, but remove any other symbols or uncommon characters from the comment. You may just want to replace all of the comment text between the : and } with filler text.
  2. DO NOT delete the line of code.
  3. Save the edited file to the desktop, be sure not to save it as a .txt
  4. If needed, right click>edit the program from the system tree and click OK when the error appears.
  5. Select File>Import
  6. Import the edited file saved on the desktop.
  7. Check to see if the changes you made have corrected the application and Save.

Method 2: May be used if the build the file was created in is significantly different than the current build.

  1. Edit the program
  2. Copy the indicated tempaut file to the desktop
  3. Install the version of SmartStruxure which the function block was created on or locate a PC at an older revision
  4. Import the files to an AS or ES at the original build
  5. Edit the program
  6. Remove the objects in error.
  7. Export the edited files and re-import in the current build
  8. Add back any removed elements that are required for the program to function.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (6)
  • Find more articles tagged with:
  • 16241
  • 26213
  • 26527
  • lines
  • missing
  • saving
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore