Issue
In EBO 2022 or higher the "Semantic Engineering View" button is grayed-out in EBO WorkStation and "Semantic DB authentication failure" is shown in Alarm View.
"Semantic Engineering View" button is grayed-out and "Semantic DB authentication failure" alarm
Product Line
EcoStruxure Building Operation
Environment
Building Operation Workstation
Cause
EBO user that connects to the Sparql database has the wrong username and/or password.
Resolution
Make sure that the user configured in EBO semantic settings matches the user created in the GraphDB web interface.
- In WorkStation, in the System Tree pane, select the EBO server.
- Click the Control Panel tab.
- Click Navigate to Sparql database, this will open the GraphDB web interface.
- Login with the admin user account.
- In the top right corner, make sure that correct repository is selected, default name is "nsp".
- Go to Setup -> Users and Access.
- Edit user "nspService".
- Set a password for the "nspService" account and make sure it has access rights to the "nsp" repository then click save.
- In EBO WorkStation control Panel, open Semantic Settings.
- Set the password for username "nspService" to match the password set in the GraphDB interface.
For more information, please refer to the GraphDB help: Secure GraphDB — GraphDB SE 9.10.0 documentation (ontotext.com)