"No such Entity" due to over-limit of work area in Menta
  • "No such Entity" due to over-limit of work area in Menta
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
‎2018-09-06 01:34 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:05 PM
When downloading the Menta file to a Xenta 300 controller, an error "No such Entity" happens.
TAC Vista
  • Vista
  • Menta
Looking into the Menta file, it seems that there is over-limit of work area of Menta.
The Menta application is not so complex. There shouldn't be such problem. The problem is due to so many time schedule entries for each time schedule block.
Each time schedule entry will occupy some memory of the controller. There are multiple time schedule blocks in the application. That's why the work area will exceed the limit.
Decrease the Max. entry number of each time schedule block to 1 or what you need. Then download the application file to Xenta controller. For more issues about "No such Entity", please refer to Vista Workstation Error: 'No such entity' in value column.
  • 5785