"Failed to Connect to Server" During Sigma Data Import to EBO
  • "Failed to Connect to Server" During Sigma Data Import to EBO
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • Gary
    Gary
‎2018-09-10 07:18 AM
Last Updated: Administrator CraigEl Administrator ‎2025-11-05 08:13 PM
When performing a Sigma data import into Building Operation, the following error appears on the Enterprise Server (ES) machine:
"Failed to connect to server"
Simultaneously, the Sigma Server service on the Sigma machine has stopped unexpectedly.
  • Sigma 4.08
  • Building Operation Workstation
The Sigma database contains a longtext.rec file with unsupported characters, which causes the Sigma Server service to crash during the import process.
Option 1: Longtext Not Required
If the Sigma longtext entries are no longer needed:
On the Sigma Server:
  1. Stop the Sigma Server service.
  2. Navigate to C:\Sigma\Data\ and delete the longtext.rec file.
  3. Restart the Sigma Server service.
  4. On the SBO ES: Retry the Sigma data import.
Option 2: Longtext Required
If longtext entries are still needed:
  1. Start the Sigma Server service.
  2. Open a Sigma client (can be on the Sigma server, SBO ES, or another machine).
  3. Log into the Sigma Operator Panel.
  4. Go to System Alarm Manager → Configure → Longtext.
  5. Review each longtext entry and remove unsupported characters.
  6. Re-enter the required longtext messages.
    • You may find backup copies in C:\Sigma\Data\Longtext.
  7. On the SBO ES: Retry the Sigma data import.
Once the unsupported characters are removed or the file is deleted, the Sigma Server service remains stable, and the data import completes successfully.
Labels (2)
  • Satchwell BAS & Sigma
Tags (3)
  • 19845
  • CraigEllis25
  • DavidChild20
100% helpful (1/1)