"Error: Sequence too complex" received when attempting to save Event Sequences

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Error: Sequence too complex" received when attempting to save Event Sequences
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1045 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Error: Sequence too complex" received when attempting to save Event Sequences

Picard Product_Support
‎2018-09-06 12:26 PM

Issue

Is there a limit on the number of action steps for a sequence?
Is there a memory limitation on the number of action steps for a sequence?
What prevents me from adding any more than 13 steps to a event sequence? 

Environment

I/NET Seven - Event Sequences

Cause

Due to memory limitations, if using any of the Output commands, you are limited to only use 12 lines items per event sequence instead of the normal 18 line items per event sequence.

An allocation of 128 bytes of memory is allocated for each sequence, adding an action sequence to a point requires 8 bytes of memory plus additional bytes for each action defined in the sequence. The memory required for each event sequence action is shown in the table below.  The system will notify you when this memory limitation is reached via this "Sequence to complex" error.

Action Memory
Required
Start
Start with Lock
Stop
Stop with Lock
Lock Door
Lock Door with lock
Inhibit alarm
Enable alarm
Event Unlock
5 bytes
Output
Output with Lock
9 bytes
Skip if Zero
Skip if Non-Zero
Unconditional Skip
6 bytes

Resolution

If your are using only the "Output with Lock" or "Output" event sequence action in one sequence, only 12 lines are allowed.  If more lines are required, the SKIP command can be used to connect as many sequences (maximum of 64 per controller) as required.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 7762
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore