bCX1 controller will not start up, the CPU LED flashes 5 times and remains on steady
  • bCX1 controller will not start up, the CPU LED flashes 5 times and remains on steady
  • PaulFr
    PaulFr
  • CraigEl
    CraigEl
‎2018-09-10 07:53 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:09 AM
After powering off, pressing the reset and Reset IP button a bCX1 controller still will not start up. CPU does not flash and controller will not respond to a ping.
Andover Continuum
  • bCX1-CR-INF 9640
  • bCX1-CR 4040
The controller is connected to an Ethernet network that is in a broadcast storm condition. This scenario can also occur if a patch lead is inadvertently looped back onto the same Switch/Router.
Disconnect the Ethernet cable from the controller and it will start up correctly.
On a very busy network or under a broadcast storm condition the controller will protect itself as detailed in Controllers go offline during a broadcast storm.
  • 8038