Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Xenta server trend logs are mixed up or missing when logged to SQL

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta server trend logs are mixed up or missing when logged to SQL
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • HenrikTarpgaard
    HenrikTarpgaard
  • David_Kendrick
    David_Kendrick
  • sesa177673
    sesa177673

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1181 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta server trend logs are mixed up or missing when logged to SQL

Picard Product_Support
‎2018-09-10 10:16 PM

Last Updated: Admiral David_Kendrick Admiral ‎2022-08-09 08:59 AM

Issue

Xenta server trend logs are mixed up or missing when logged to SQL. For example log a from Xenta server 1 is logged under log a in Xenta server 2. This causes duplicates for some logs and missing logs for others.

Product Line

TAC Vista

Environment

  • Vista 5.1.X
  • Xenta server 5.1.X with trendlogs that are retrieved by Vista and logged to SQL.

Cause

When creating the Xenta servers, copy/paste has been used in Vista. Using copy/paste causes certain references to be created incorrectly.

Resolution

!If you have already encountered the behaviour described contact Product Support! Otherwise read on...

The correct way to engineer Xenta servers in Vista when the XBuilder project is to be reused.

  1. Right-click on the server object in Vista and select New->Xenta Server X5\7\9xx
  2. Right-click the newly created Xenta server and select Edit
  3. In the XBuilder project that opens, configure and download your project to the Xenta server.
  4. Close the XBuilder and save the changes to the current project when prompted.
  5. Refresh Vista and ensure that everything is online and correct in the Xenta server.

To reuse this project in another Xenta server

  1. Right-click the Xenta server in Vista and select Edit.
  2. Make the appropriate changes to the project e.g. change the IP address.
  3. You can now either save the project as a template or choose Save as from the file menu.
  4. Rename the file and save it.
  5. After saving, select the menu item Vista Database->Save As and navigate to the Vista server object in the dialogue that opens.
  6. Right-click in the dialogue window and select New->Xenta Server X5\7\9xx.
  7. Choose an appropriate name and then click on Select.
  8. Go to Vista workstation and update the server object. The new Xenta server should now appear.

Now it has been created it can be edited further and then downloaded to via XBuilder.

 

Note: If the trend log values are mixed up also in the Xenta Server itself (i.e. in a trend log page) it may be a different issue, see Trend log values from M-bus meters under a Xenta Server are mixed up.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 7676
  • DavidKendrick22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of