Xenta 913 will not communicate with a Bacnet IP device
  • Xenta 913 will not communicate with a Bacnet IP device
  • PeterLarsen
    PeterLarsen
‎2018-09-06 01:14 PM
Xenta 913 will not communicate with the Bacnet device.
Wireshark does not show any packets between 913 and Bacnet device
Xenta 913
The Xenta 913 has been installed on a TCP/IP network with a switch between the Xenta 913 and Bacnet device.
A basic switch does not pass broadcast messages that a Xenta 913 uses to talk to Bacnet device.
The solution to this issue is to replace the switch with a Hub or use a managed switch.
If a managed switch is used it will need to be configured to pass broadcast messages from the Xenta 913 to the Bacnet device.
Labels (2)
  • TAC INET
  • 6293